is it possible to have 2 automatic transfer switches within the same circuit?

Presently i have an automatic transfer switch between the generator and shore power, and a manual switch between those circuits and the inverter, then to main panel.

i would like it to be automatic in both cases. thoughts?

i will post this on 2 other sites just in case you might see my question there also.


Tim
Sue and Tim
4 REPLIES 4

tlaffourtit
Nomad
Nomad
thanks for your thoughts. i will remove the one manual and add the second ats.
Sue and Tim

tlaffourtit
Nomad
Nomad
tks housted
Sue and Tim

Housted
Explorer III
Explorer III
I converted my 30 amp coach to 50 amp when I installed the cord reel.
I have 2 auto transfer switches.
A 50 amp for the shore power and all else that feeds the breaker panel.
A 30 amp (existing)to transfer from gen set to inverter and feeds the 50 amp switch.
Totally automatic transfer!!:B
One thing to be aware of is the fact that you will have 2 delays stacked.
This caused some concern when I first tested!!:o

Housted