Boon Docker wrote:Good point but very few posters know their % loss. While connecting to remote wires can be a good solution the compromise is that the CC MAY not know the actual battery voltage because the CC does not have remote voltage sense.CA Traveler wrote:
Charging will be compromised from very small to unacceptable. Wire size, length and amperage (ie solar size) are the main considerations.
The factory wire size would have to be very small to be unacceptable. I don't think that they install wire quite that small between the converter and battery.
My 200 watt system with a 15 foot run from converter (where charge controller output is connected) has a .50 % loss at full output.
A 400 watt system would have a 1.0 % loss.
A 600 watt system would have a 1.5 % loss.
All very acceptable.
โSep-01-2017 08:42 PM
joel1 wrote:That's a common scenario and doesn't stand the test of good sealing.
I could do that just wanted to avoid drilling any holes on the roof.
โSep-01-2017 08:24 PM
โSep-01-2017 05:01 PM
โSep-01-2017 04:38 PM
โSep-01-2017 04:30 PM
โSep-01-2017 04:13 PM
โSep-01-2017 03:34 PM
CA Traveler wrote:
Charging will be compromised from very small to unacceptable. Wire size, length and amperage (ie solar size) are the main considerations.
โSep-01-2017 02:49 PM
joel1 wrote:You should have a DC breaker (fuse is 2nd choice) between the solar panel and the controller. Many/most controllers will smoke if the panel is connected when the battery isn't. A breaker can serve as a switch (a fuse is more hassle) so you can disconnect the solar before working on the controller or battery. And you can get a DC breaker for about the same cost as a switch, if you're willing to wait a couple/three weeks to get it.
Thanks for the input guys. At which area would you add the DC breaker or fuse?