FunnyCamper wrote:In all cases a DVM is your friend as you want good voltage for ACs and especially when you use both plugs on the pedestal. I'm always suspicious that a 30/20 pedestal is wired for 30A and not a 50A draw.
wow. good electrical info for me.
our state parks are mostly 30 amp pedestal with a 15 amp plug included on the stand. I was hoping to plug into the 30 amp and run just one of my main ac and then the separate garage I would run into the 15 amp plug. that is when the service guy said don't do that ๐ only a 20 amp plug will be good enough for that 13.5 ac in the garage.
I will check each of my state parks I love and ask exactly what power is on that pedestal. I know the 30 amp plug is there, but will ask what the amps are on the smaller plug. hopefully 20 amp would be sweet to hear is included.
โSep-17-2013 04:17 AM
โSep-16-2013 03:56 PM
SpencerRB wrote:3 ACs will not trip the CB on 50A unless they are wired on the same leg which would not be the best balance of loads.
Maybe I'm mistaken regarding the load management feature on the triple A/C trailers. Maybe it is only used when attempting to run multiple A/C's off the genny, but if my memory serves me correctly, I've read some people having issues running all 3 at the same time when plugged into 50 amp service.
โSep-16-2013 03:49 PM
โSep-16-2013 03:39 PM
allcool wrote:SpencerRB wrote:
I believe he has 50 amp on the trailer. He was adding a 20 or 30amp separate circuit for the 3rd A/C separate from the trailer electrical.
You do bring up an interesting point. From my understanding, 50amp service is actually rated at 240v, so at 120v, it is rated at 100amps. If this is the case, why do 50amp trailers need load management devices to handle 45 amps (3 15k) of A/C units? This should be less than half of total capacity.
Not exactly...
Its 25amps at 240v and 50amp at 120v.
100amps at 120v would be 12,000 watts, not happening on a Onan5500, ever.
If you measure between both legs of 120v it will be 240v on the 5500 genny. Either 240v leg measured to neutral or ground, gives 120v.
Thats why there are 2, 30 amp breakers, one for each 120v leg of the 240 being produced by the genset. Each leg is good for a little less than 25amps @120v, more or less. So thats how it gets a rating of 50amps, 2 separate 25amp 120v circuits. Actual specs, its 45.8 amps, so in reality, each 120v leg is rated for 22.9amps constant draw...
Make no mistake, 5500 watts is 5500 watts, no matter what voltage. 5500w, thats all we get out of the Onan 5500. Although a surge to 6000watts momentarily will happen.
โSep-16-2013 03:29 PM
allcool wrote:SpencerRB wrote:
I believe he has 50 amp on the trailer. He was adding a 20 or 30amp separate circuit for the 3rd A/C separate from the trailer electrical.
You do bring up an interesting point. From my understanding, 50amp service is actually rated at 240v, so at 120v, it is rated at 100amps. If this is the case, why do 50amp trailers need load management devices to handle 45 amps (3 15k) of A/C units? This should be less than half of total capacity.
Not exactly...
Its 25amps at 240v and 50amp at 120v.
100amps at 120v would be 12,000 watts, not happening on a Onan5500, ever.
If you measure between both legs of 120v it will be 240v on the 5500 genny. Either 240v leg measured to neutral or ground, gives 120v.
Thats why there are 2, 30 amp breakers, one for each 120v leg of the 240 being produced by the genset. Each leg is good for a little less than 25amps @120v, more or less. So thats how it gets a rating of 50amps, 2 separate 25amp 120v circuits. Actual specs, its 45.8 amps...
Make no mistake, 5500 watts is 5500 watts, no matter what voltage. 5500w, thats all we get out of the Onan 5500. Although a surge to 6000watts momentarily will happen.
โSep-16-2013 03:04 PM
SpencerRB wrote:
I believe he has 50 amp on the trailer. He was adding a 20 or 30amp separate circuit for the 3rd A/C separate from the trailer electrical.
You do bring up an interesting point. From my understanding, 50amp service is actually rated at 240v, so at 120v, it is rated at 100amps. If this is the case, why do 50amp trailers need load management devices to handle 45 amps (3 15k) of A/C units? This should be less than half of total capacity.
โSep-16-2013 01:51 PM
โSep-16-2013 01:11 PM
SpencerRB wrote:
I believe he has 50 amp on the trailer. He was adding a 20 or 30amp separate circuit for the 3rd A/C separate from the trailer electrical. Thanks
You do bring up an interesting point. From my understanding, 50amp service is actually rated at 240v, so at 120v, it is rated at 100amps. If this is the case, why do 50amp trailers need load management devices to handle 45 amps (3 15k) of A/C units? This should be less than half of total capacity.It's a 240/120V circuit and since few RVs have 240V appliances most think of it as 2 50A circuits. That's a lot of power and will run everything including 3 ACs. For this load management is not needed.
But load management does play a part for 20A and 30A pedestals and the gen.
โSep-16-2013 11:52 AM
CA Traveler wrote:
Have you considered upgrading to a 50A service? Then you could run all 3 ACs and the MW, HW and hair dryer all at the same time. Of course you would need a 50A site.
There are various ways to accomplish this.
Another option is a 50A to 2 30A plugs, one for the current plug and the second one for everything the daughter needs.