Rich D. wrote:dougrainer wrote:djedgar wrote:
Thank you for the replies. We are now looking at a new unit since newer ones are more efficient and have better output. I am sure the reversing valve coil is OK as it does click when I connect and disconnect a lead wire.
As for the valve default being heat, I get the same temp out of the vents (pretty much ambient temperature) whether I set the control to 80 plus degrees or 65. The reversing valve I suspect even though getting energized, does not fully slide over (but does move some based on the magnet attraction point moving). All three of the copper tubes coming out the top of the reversing valve are equal in temp as far as feeling them goes.
We are also considering replacing both roof units. The bedroom one still works fine but by replacing both, I can run the newer 12 button control and not have to worry about buying a downgrade kit. Would amount to an extra thousand dollars over all but would have better performance and efficiency.
By the way, the sale at Camping World did not work out for us as they packaged it with the distribution box, which we do not need since we have ducts.
The NEW Penguins are NOT 15k units. Dometic no longer have 15k Penguins. They have the 13.5k and what Dometic calls a HC. The HC is NOT 15k, but larger than a 13.5k and slightly less than a 15k. BUT NOT 15K. I doubt you could tell the difference, but just wanted to let you know. The New Penguins come with the 12 button control onboard, so the only extra cost would be the wall 12 button tstat. IF the price is correct, just throw the distribution box kit away. Doug
What is with that BTU rating?
From their website:
11,000, 13,500 or high capacity BTUs
Then in their specifications one paragraph down:
Capacity range of this series (BTUs) 11,000/13,500/15,000
http://www.dometic.com/enus/Americas/USA/RV-Products/climate/ac-display-page/?productdataid=66930
โAug-05-2013 06:49 AM
dougrainer wrote:djedgar wrote:
Thank you for the replies. We are now looking at a new unit since newer ones are more efficient and have better output. I am sure the reversing valve coil is OK as it does click when I connect and disconnect a lead wire.
As for the valve default being heat, I get the same temp out of the vents (pretty much ambient temperature) whether I set the control to 80 plus degrees or 65. The reversing valve I suspect even though getting energized, does not fully slide over (but does move some based on the magnet attraction point moving). All three of the copper tubes coming out the top of the reversing valve are equal in temp as far as feeling them goes.
We are also considering replacing both roof units. The bedroom one still works fine but by replacing both, I can run the newer 12 button control and not have to worry about buying a downgrade kit. Would amount to an extra thousand dollars over all but would have better performance and efficiency.
By the way, the sale at Camping World did not work out for us as they packaged it with the distribution box, which we do not need since we have ducts.
The NEW Penguins are NOT 15k units. Dometic no longer have 15k Penguins. They have the 13.5k and what Dometic calls a HC. The HC is NOT 15k, but larger than a 13.5k and slightly less than a 15k. BUT NOT 15K. I doubt you could tell the difference, but just wanted to let you know. The New Penguins come with the 12 button control onboard, so the only extra cost would be the wall 12 button tstat. IF the price is correct, just throw the distribution box kit away. Doug
โAug-04-2013 04:44 AM
djedgar wrote:
Thank you for the replies. We are now looking at a new unit since newer ones are more efficient and have better output. I am sure the reversing valve coil is OK as it does click when I connect and disconnect a lead wire.
As for the valve default being heat, I get the same temp out of the vents (pretty much ambient temperature) whether I set the control to 80 plus degrees or 65. The reversing valve I suspect even though getting energized, does not fully slide over (but does move some based on the magnet attraction point moving). All three of the copper tubes coming out the top of the reversing valve are equal in temp as far as feeling them goes.
We are also considering replacing both roof units. The bedroom one still works fine but by replacing both, I can run the newer 12 button control and not have to worry about buying a downgrade kit. Would amount to an extra thousand dollars over all but would have better performance and efficiency.
By the way, the sale at Camping World did not work out for us as they packaged it with the distribution box, which we do not need since we have ducts.