Remove 50amp genset and replace with 50 shore power
highlife4me
Since I have a 96 class A with a 30 amp service but a 50 amp genset that would run both AC units. I would like to remove the generator and wire in a 50 amp shoreline so I can run everything. Does anyone see a problem doing this as long as the proper materials are used?
23 REPLIES 23
highlife4me
Going to sell generator since its never used and needs some work. Why carry that extra weight and take up the space, Maybe put a small air compressor in its place.
wolfe10
Bill S. wrote:
^^^ This ^^^, what Dutch said. It will be simple, inexpensive, and you will have the best of both worlds; you'll have both A/C's when on shore power, and still have the generator, which powers everything already. The only new procedure will be you will have 2 cords to plug in to the pedestal; the existing 30A shorepowr cord, and the newly added 20A service which you'll simply plug in to oneof the 20A/120V receptacles in the power pedestal.
Yup, a viable "work around" to true 50 amp wiring.
BTW, very unusual to have a 7KW generator with 30 amp wiring.
Brett Wolfe
Ex: 2003 Alpine 38'FDDS
Ex: 1997 Safari 35'
Ex: 1993 Foretravel U240
Bill_S_1
Bill, (aka Capt.Bill)
2002 Horizon 36LD, Cat 330
RVing since 1987
First State
highlife4me
looks like several options. Thanks All
Dutch_12078
There's a simpler way to get power to both A/C's that works even on most 30 amp sites. It involves determining which hot and neutral in the generator wiring junction box feeds the second A/C. That pair is brought out to a 20 amp plug and socket that can be unplugged to connect a 12 ga extension cord that plugs into the 20 amp utility outlet found on most campsite panels.
Dutch
2001 GBM Landau 34' Class A
highlife4me
Onan Marquis 7000 watt generator
MrWizard
Moderator
Moderator
30 amp shore cord and breaker panel
One each hot, neutral, ground 10 gauge wire
Generator possible wiring, very common
One neutral, one ground , two hots
One hot goes to ts stitch and breaker panel for 30 amps
Second hot goes only goes only too the second a/c
50 amp shore power
One neutral, one ground, two hots, all wires are 6 gauge
It is 50 amps on each hot, 100 amps total
This has nothing to do with removing the generator
You can Not just remove generator and splice wires to new shore cord
You need new breaker panel, new wire from panel to the New TS, all the way to the New shore connection
I can explain it to you.
1997 F53 Bounder 36s
wolfe10
Sorry, makes no sense. If 50 amp generator (never heard of them being rated in amps) why not just leave the generator in place and replace:
Shore power cord
Wiring from shore power cord to ATS (assume you have an ATS-- if not to a new outlet that generator can be plugged into)
New wiring from ATS to main 120 VAC breaker box
New breaker box with 240 VAC/two HOTS inputs.
This AIN'T for the faint of heart or on a small budget. There are other options, but this would be the "automatic way"-- the way a 50 amp coach would have been wired from the factory.
Brett Wolfe
Ex: 1997 Safari 35'
2oldman
just to verify, what is the make and model of the gen?