hypoxia wrote:
I suggest a duel at sunrise between the Texan & Douggrainer.:B On a more serious note, both are excellent sources of information & we are fortunate to have them here. Personally I would go with two 15K units.
โAug-08-2013 06:03 PM
โAug-08-2013 03:26 PM
CyberSanford wrote:
Thanks DougRainer
I was told by my original installer about turning the thermostat back a little. I just thought this ac was built to run and to turn back the temp kinda defeats the purpose of getting it cold inside. But I guess if I have to.
So do you think I had a choice regarding the freeze control device? Did I need to ask for that?
thanks
Mark
When the outdoor temperatures drop in the evening to below 75ยฐF, the temperature control should be set midway between WARMER and COOLER. Otherwise the evaporator coil may become iced up and stop cooling. Should icing up occur, it is necessary to turn the air conditioner off for at least 45 minutes to clear the coil of ice. Alternatively, you may turn the selector to the HI FAN position until increased airflow is observed.
โAug-08-2013 01:57 PM
โAug-08-2013 01:30 PM
The Texan wrote:dougrainer wrote:Sorry Doug, but I hold a Journeyman Electrician license and I will guarantee you my dogbone is NOT burnt or corroded. I know what my system is doing at all times and with BOTH 13.5 Dometic AC's running, even when they both have a compressor start at the same time, it does NOT exceed 30A.The Texan wrote:dougrainer wrote:Doug, go back and read his post. He said ONE 15k on 30A, NOTHING about running both on 30A. And like I said we are setting here with temps reaching low 90s and have no problems with two 13.5k Dometic on 30A. Yes, we do shut down the rear AC when we run the micro and we do have the water heater on gas, but we have a residential fridge, a 32" TV and all the other normal stuff. We have NOT tripped a ckt breaker once.The Texan wrote:
We are running BOTH 13.5 units on 30A with NO problems, so you will have no problem with a 15 unit. Try running your fan on "high" instead of auto, when in high humidity and that should stop the icing.
Really??? If you look at his photo post, his 13.5 Penguin will pull 15.1 amps at 95 degree ambient on hi cool. His 15k original rear unit will pull 16.1 amps on hi cool at 95 degrees. That puts his TOTAL AC load at 31.2 amps with NOTHING else in his RV on. If the temps go to 105 (they are in Texas right now), his amp draw will go UP 2 more amps to a total of 33.2 amps. Doug
NO, YOU read it again. I see nothing in his post about running his RV on 30 amp service. YOU made the statement about your RV on 30 amp service and I was just letting him know, that almost ALL RV's cannot run 2 AC units on 30 amp service especially his. I will bet if I look at your 50 to 30 adapter, it is burnt and corroded (30 amp side) from the excess amp draw caused by what you are doing. Doug
Here is his post I referred to, that you say did NOT exist...TexasRedNeck wrote:
Regarding the 30 vs 50 amp, I will use 50 amp sites until the fall and hope that 30 amp will run the 15K unit in the main living area and be enough without cranking up the second AC. I think the 15k AC pulls about 17A at start up if I recall correctly.
โAug-08-2013 12:03 PM
โAug-04-2013 06:17 PM
dougrainer wrote:Sorry Doug, but I hold a Journeyman Electrician license and I will guarantee you my dogbone is NOT burnt or corroded. I know what my system is doing at all times and with BOTH 13.5 Dometic AC's running, even when they both have a compressor start at the same time, it does NOT exceed 30A.The Texan wrote:dougrainer wrote:Doug, go back and read his post. He said ONE 15k on 30A, NOTHING about running both on 30A. And like I said we are setting here with temps reaching low 90s and have no problems with two 13.5k Dometic on 30A. Yes, we do shut down the rear AC when we run the micro and we do have the water heater on gas, but we have a residential fridge, a 32" TV and all the other normal stuff. We have NOT tripped a ckt breaker once.The Texan wrote:
We are running BOTH 13.5 units on 30A with NO problems, so you will have no problem with a 15 unit. Try running your fan on "high" instead of auto, when in high humidity and that should stop the icing.
Really??? If you look at his photo post, his 13.5 Penguin will pull 15.1 amps at 95 degree ambient on hi cool. His 15k original rear unit will pull 16.1 amps on hi cool at 95 degrees. That puts his TOTAL AC load at 31.2 amps with NOTHING else in his RV on. If the temps go to 105 (they are in Texas right now), his amp draw will go UP 2 more amps to a total of 33.2 amps. Doug
NO, YOU read it again. I see nothing in his post about running his RV on 30 amp service. YOU made the statement about your RV on 30 amp service and I was just letting him know, that almost ALL RV's cannot run 2 AC units on 30 amp service especially his. I will bet if I look at your 50 to 30 adapter, it is burnt and corroded (30 amp side) from the excess amp draw caused by what you are doing. Doug
TexasRedNeck wrote:
Regarding the 30 vs 50 amp, I will use 50 amp sites until the fall and hope that 30 amp will run the 15K unit in the main living area and be enough without cranking up the second AC. I think the 15k AC pulls about 17A at start up if I recall correctly.
Bob & Betsy - USN Aviation Ret'd '78 & LEO Ret'd '03 & "Oath Keeper Forever"
โAug-04-2013 05:56 PM
CyberSanford wrote:
Could I butt in here for a bit. This topic is exactly my AC problem. And yall seem to know spefics of these ac's. I mean detailed specifics i am impressed and really hoping yall can tell me which way i should go. I am ready to pull my hair out...
I have a 1997 33' Airstream Land Yacht motorhome. 30 amp can only run one ac at a time on shore power. But on generator with 30 amp breaker i can run both. Thats not my problem but from what Doug said about not good to run both on 30 amp i might stop.
Here is my question/problem. Both are NON DUCTED, I Have 13.5 penquin low profile in back bedroom/bath. Works great. Originally had same thing in front. But with all the windows and front windshield its an oven up there. So I swapped it out for 15k btu low profile. I have had both dometic and currently have coleman mach8 low profile. Both of these new 15k btu's have been lowprofile. These 15k btu's are freezing up at night. Houston and Dallas. Compressor makes aweful noise. Air blowing out cuts to a trickle and its hot air most of the time water drips out, quite a bit(I am guessing this is freezing up). I keep my fan speed on high always.
I read either on this thread or another someone was using a dehumidifier ....?
I had a rv tech tell me he has swapped out several 1-2 year old low profiles and installed fullsize units specifically because the lowprofiles kept freezing up.
What say you experts? Do you have some questions of my setup to help me make a good decision? What unit should I get? Size? Brand name? Model?
I am all ears. I need help
If you read this far thanks for your time
Mark
โAug-04-2013 05:15 PM
โAug-01-2013 04:51 AM
The Texan wrote:dougrainer wrote:Doug, go back and read his post. He said ONE 15k on 30A, NOTHING about running both on 30A. And like I said we are setting here with temps reaching low 90s and have no problems with two 13.5k Dometic on 30A. Yes, we do shut down the rear AC when we run the micro and we do have the water heater on gas, but we have a residential fridge, a 32" TV and all the other normal stuff. We have NOT tripped a ckt breaker once.The Texan wrote:
We are running BOTH 13.5 units on 30A with NO problems, so you will have no problem with a 15 unit. Try running your fan on "high" instead of auto, when in high humidity and that should stop the icing.
Really??? If you look at his photo post, his 13.5 Penguin will pull 15.1 amps at 95 degree ambient on hi cool. His 15k original rear unit will pull 16.1 amps on hi cool at 95 degrees. That puts his TOTAL AC load at 31.2 amps with NOTHING else in his RV on. If the temps go to 105 (they are in Texas right now), his amp draw will go UP 2 more amps to a total of 33.2 amps. Doug
โAug-01-2013 04:45 AM
TexasRedNeck wrote:dougrainer wrote:
copy and paste this link to see the options on a Penguin model. Doug
http://www.dometic.com/2664aef6-0859-4c05-93f2-f4e20fecbb1a.fodoc
Doug, thanks for the link. Unfortunately I don't see the same numbers that appear on my label. I'm really not trying to be obtuse.
โJul-31-2013 09:16 PM
dougrainer wrote:Doug, go back and read his post. He said ONE 15k on 30A, NOTHING about running both on 30A. And like I said we are setting here with temps reaching low 90s and have no problems with two 13.5k Dometic on 30A. Yes, we do shut down the rear AC when we run the micro and we do have the water heater on gas, but we have a residential fridge, a 32" TV and all the other normal stuff. We have NOT tripped a ckt breaker once.The Texan wrote:
We are running BOTH 13.5 units on 30A with NO problems, so you will have no problem with a 15 unit. Try running your fan on "high" instead of auto, when in high humidity and that should stop the icing.
Really??? If you look at his photo post, his 13.5 Penguin will pull 15.1 amps at 95 degree ambient on hi cool. His 15k original rear unit will pull 16.1 amps on hi cool at 95 degrees. That puts his TOTAL AC load at 31.2 amps with NOTHING else in his RV on. If the temps go to 105 (they are in Texas right now), his amp draw will go UP 2 more amps to a total of 33.2 amps. Doug
Bob & Betsy - USN Aviation Ret'd '78 & LEO Ret'd '03 & "Oath Keeper Forever"
โJul-31-2013 07:30 PM
dougrainer wrote:
copy and paste this link to see the options on a Penguin model. Doug
http://www.dometic.com/2664aef6-0859-4c05-93f2-f4e20fecbb1a.fodoc