TomTHaullie wrote:
So do you know if I need to get the Dino Fan50 board or the small, form universal ignition board? The chart says Fan50, but so many other links say the UIB S is my replacement.
โJan-10-2016 03:31 PM
โJan-10-2016 02:45 PM
TomTHaullie wrote:
Thank you for all the responses so far!
Been connected to shore power since October. No issues anywhere in rig with the 12v system. When fan straight wired to battery, runs at speed. Board and fan getting 12.39v to them. There is a discoloration at the motor connector on the board .... probably from short.
New info .... when cabin comes to temp, flame shuts off, fan slows, and LED flashing/clicking atarts. I waited 5 minutes with mo change. When I bump thermostat to higher temp, fan speds ip and flame does not come on. Clicking stops. Blows cold air until I turn off system at thermostat or outside switch. Reset outside, and it will cycle and flame/heat once. Repeat.
All I am reading suggests that there is a board control issue with fan control or flame sensing or something around that part of cycle. I will take board to dealer tomorrow and have tested.
โJan-10-2016 12:52 PM
โJan-10-2016 12:40 PM
joebedford wrote:
Do you have the thermostat fan control set to auto?
โJan-10-2016 12:14 PM
โJan-10-2016 11:40 AM
Old-Biscuit wrote:
The circuit broad has a 'blower power'........old timed delay relay incorporated onto board
T-stat calls for heat
Fan gets power thru circuit board
Fan comes up to speed......sail switch makes up/high temp limit switch already closed...power goes back to board and then to gas valve/ignitor
Heats blows......
T-stat set point gets satisfied....t-stat contacts open
Power to gas valve gets dropped
Fan continues to run until 'blower power' shuts down
Fan not shutting down.......
Bad contact on connector at board. Pull/clean board contact surface with pencil eraser and check that pins in connector are not bent
OR
bad 'blower power'..........NEW board
Low battery ,,,,,,,,,
Fan would not start and if it did it wouldn't come up to high enough speed to move enough air to satisfy sail switch.
Gas valve wouldn't stay open....heating wouldn't happen
โJan-10-2016 11:20 AM
โJan-10-2016 11:03 AM
โJan-10-2016 08:25 AM
fischer wrote:
the board has a time delay for turning the gas valve on/off.Also the fan delay for turning the fan off. Here is the link for troubleshooting you furnace. The first thing a all techs do is check all connections on the board also battery should be fully charged. http://bryantrv.com/docs.html
โJan-10-2016 08:03 AM
โJan-10-2016 05:48 AM