smkettner wrote:Don't bother with the 1000w genny and either get the WFCO to work properly or replace it with something that will ie Iota or Progressive Dynamics. To the OP, is the WFCO charging your batteries? How long does it take?
mena661, what do you recommend?
โOct-21-2012 06:39 PM
โOct-21-2012 06:34 PM
smkettner wrote:I think that's part of the point BFL was making. Who wants to run a genny for 4 hrs just to charge batteries? Might as well just run off the genny period.
Forever is a long time. 30 amps will charge one or two batteries to 90% in 2 to 4 hours.... a lot less than forever.
โOct-21-2012 05:14 PM
BFL13 wrote:
If you get a small enough (low amp instead of 55amp) charger to run on the "1000w" gen, the amps will be so low it will take forever to charge the battery bank.
โOct-21-2012 05:06 PM
โOct-21-2012 04:58 PM
โOct-21-2012 04:55 PM
BFL13 wrote:
A 100w panel will do maybe 6amps mid-day, less earlier and later. 6 amps is two double lamps worth of Rv use--ie not a whole lot. It will certainly help (when the sun is out and you are in the open), but it is not a game changer between a 1000w and a 2000w gen IMO.
If you have a mix of gen/charger and solar, the idea is to do a fast charge with the gen in the morning and let the solar do the rest all day at its low amps before you hit the batts from supper through movies till bedtime and maybe some furnace at night.
That means the 2000w gen and a high amp charger for the short time gen part. It makes no sense to have a long low amp gen run and then a short period of solar at even lower amps.
โOct-21-2012 04:35 PM
โOct-21-2012 04:09 PM
BFL13 wrote:
The converter has a power factor of about 0.7, so that 950w input will pull about 1357VA from the gen continuous. That is nearly the continuous rating of the "2000w" gen.
If you get a small enough (low amp instead of 55amp) charger to run on the "1000w" gen, the amps will be so low it will take forever to charge the battery bank.
IMO don't even think about getting a 1000w gen for running a battery charger. It will have to run so long to get the batteries up, you might as well just stay on the gen all day and not run the batteries down in the first place ๐
โOct-21-2012 03:53 PM
โOct-21-2012 03:47 PM
ZZSPIRAL1 wrote:Longer charge times.
What's the downside of a smaller converter? .