DIY 50 amp to 20 amp pigtail

KnowNuthin
Explorer
Explorer
I want to plug my tractors block heater into our 50 amp RV service for the upcoming winter monthsโ€ฆ

Our panel has 1 - 50 amp and 2 - 20 amp breakersโ€ฆ both 20 services are taken and currently used year roundโ€ฆ (chicken heat lamps, water bowl heaters etc.)โ€ฆ

What Iโ€™m envisioning is a 50 amp plug with a 3 wire pigtail connected to the common, neutral and one hot legโ€ฆ leaving the second hot leg vacantโ€ฆ

This would give me 120v 50 amp at the pigtail endโ€ฆ no?

This would be used STRICTLY for a 600 watt engine block heaterโ€ฆ

Is this a bad, terrible or workable idea?
2005 2500HD D/A CC LB 4X4 being pushed by:
2016 Grand Design Reflection 303RLS
2007 Ural GearUp Arctic
60 REPLIES 60

Grit_dog
Navigator
Navigator
toedtoes wrote:


That works. If this is going to be a yearly need, you could size the cut to exactly the length needed. I'd say take a 50ft cord and make two 15 feet and a 20 foot from it - that gives you a couple shorter cords for when you are RVing.


Or NOT do what some people think is a good idea (hacking a perfectly good expensive waterproof cord into multiple chunks) and just put it in a bucket or cover the cord from UV if it's sitting outside all year.

Especially since it was established in the first post that there is no need for any sort of "HD" power cord anyway (to run the block heater on the tractor).
2016 Ram 2500, MotorOps.ca EFIlive tuned, 5โ€ turbo back, 6" lift on 37s
2017 Heartland Torque T29 - Sold.
Couple of Arctic Fox TCs - Sold

toedtoes
Explorer III
Explorer III
KnowNuthin wrote:
My tractor is parked next to the wall where the electric service is locatedโ€ฆ less than 10โ€™โ€ฆ. My shortest HD extension cord is 50โ€™โ€ฆ

Part of the reasoning behind my original idea was so II could plug a custom length cord directly into the outletโ€ฆ

I might just cut one of my cords in half and get two replacement ends to create shorter cordsโ€ฆ the 50โ€™ one Iโ€™m using for my diesel pickup block heater gets warm when usedโ€ฆ


That works. If this is going to be a yearly need, you could size the cut to exactly the length needed. I'd say take a 50ft cord and make two 15 feet and a 20 foot from it - that gives you a couple shorter cords for when you are RVing.
1975 American Clipper RV with Dodge 360 (photo in profile)
1998 American Clipper Fold n Roll Folding Trailer
Both born in Morgan Hill, CA to Irv Perch (Daddy of the Aristocrat trailers)

KnowNuthin
Explorer
Explorer
Grit dog wrote:
Gittin a little deep and off topic for a simple plug in your block heater question that the conundrum has been solved already.


I belong to another, motorcycle related web board where I, along with seven others, perform the job of moderatorโ€ฆ

Iโ€™ve come to the realization that, Eventually, โ€œOff topicโ€ is standard operating procedure in most threadsโ€ฆ if the OP continually brings the focus back to center the thread will live on with much relevant information brought forthโ€ฆ

As moderator, I humorously pointed out to one of our newer members that the official record was five posts before the thread went completely off the railsโ€ฆ gave him the advice: โ€œkeep bringing things back to your original issue and ignore the โ€˜fluffโ€™โ€ฆโ€

I guess we should be thankful we got well into page 3 before things began to go sidewaysโ€ฆ

โ€ฆand, yes, Iโ€™m thankful to all those more electrically knowledgeable than myself who kept me from frying my barn/tractor/electrical systemโ€ฆ
2005 2500HD D/A CC LB 4X4 being pushed by:
2016 Grand Design Reflection 303RLS
2007 Ural GearUp Arctic

Grit_dog
Navigator
Navigator
Gittin a little deep and off topic for a simple plug in your block heater question that the conundrum has been solved already.
2016 Ram 2500, MotorOps.ca EFIlive tuned, 5โ€ turbo back, 6" lift on 37s
2017 Heartland Torque T29 - Sold.
Couple of Arctic Fox TCs - Sold

wa8yxm
Explorer III
Explorer III
Bobbo wrote:
ktmrfs wrote:
the lamps are likely using a 14 or 16 ga wire, entirely capable of handling 15 or 20A for a short period of time if the lamp were to cause a short. A 12Ga extension cord is NOT capable of handling 50A for any length of time.

Nope. It is 18g.


Even 18 ga in air (not buried in a wall) can handle 20 amps plus long enough to trip a breaker or blow a fuse.

You need to understand the difference between air and insulation.,
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

Bobbo
Explorer II
Explorer II
ktmrfs wrote:
the lamps are likely using a 14 or 16 ga wire, entirely capable of handling 15 or 20A for a short period of time if the lamp were to cause a short. A 12Ga extension cord is NOT capable of handling 50A for any length of time.

Nope. It is 18g.
Bobbo and Lin
2017 F-150 XLT 4x4 SuperCab w/Max Tow Package 3.5l EcoBoost V6
2017 Airstream Flying Cloud 23FB

rhagfo
Explorer III
Explorer III
enblethen wrote:
Your 50 amp should be a double pole breaker.
I think it is a bad idea for what you are thinking.
I would suggest getting thin breaker with two 20-amp breakers and installing a new receptacle. Some call breakers, wafer or tandem.



X2!
Best, safest way to go!
Russ & Paula the Beagle Belle.
2016 Ram Laramie 3500 Aisin DRW 4X4 Long bed.
2005 Copper Canyon 293 FWSLS, 32' GVWR 12,360#

"Visit and Enjoy Oregon State Parks"

wa8yxm
Explorer III
Explorer III
LittleBill wrote:
so do all you guys who have 15 amp circuits in your house, where your lamps are plugged in use a 1 amp circuit breaker to each individual lamp?


Most all the lamps I've seen are wired with 15 amp wire and thus need nothing smaller.

Some lamps (Like Christmas tree lamps) have smaller wire.
And generally fuses in the plug body.

18 ga (Lamp cord) in open air has no problem with 15 amps for short runs.
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

KnowNuthin
Explorer
Explorer
My tractor is parked next to the wall where the electric service is locatedโ€ฆ less than 10โ€™โ€ฆ. My shortest HD extension cord is 50โ€™โ€ฆ

Part of the reasoning behind my original idea was so II could plug a custom length cord directly into the outletโ€ฆ

I might just cut one of my cords in half and get two replacement ends to create shorter cordsโ€ฆ the 50โ€™ one Iโ€™m using for my diesel pickup block heater gets warm when usedโ€ฆ
2005 2500HD D/A CC LB 4X4 being pushed by:
2016 Grand Design Reflection 303RLS
2007 Ural GearUp Arctic

toedtoes
Explorer III
Explorer III
If you are using anextension cord, you might use your 50amp extension cord from the outlet, then put the pigtail(s) at the end of the cord. That way you'll have a 50amp gauge cord for most of the length.
1975 American Clipper RV with Dodge 360 (photo in profile)
1998 American Clipper Fold n Roll Folding Trailer
Both born in Morgan Hill, CA to Irv Perch (Daddy of the Aristocrat trailers)

Grit_dog
Navigator
Navigator
KnowNuthin wrote:
Grit dog wrote:


There are a few options, not entirely clear without seeing your sub panel, but seems the easiest and safest no brainer is get a 30-20A pigtail and not ever touch the hot side of the box.

This is the Load center I haveโ€ฆ

There are a couple vacant slots still available for future circuitsโ€ฆ howeverโ€ฆ itโ€™s currently 16 degrees outside with snow forecast for the next few daysโ€ฆ

Iโ€™m trying to make this a plug-and-play scenario for nowโ€ฆ a plug in 50a adapter and an extension cord makes my time away from a cozy fire much lessโ€ฆ


Lol, I'd do the same if it's already winter!
Wow, 16 deg on the Front Range already?
But you're right, looks like it would be no problem to add another circuit in the future real easy for some more convenience power.
2016 Ram 2500, MotorOps.ca EFIlive tuned, 5โ€ turbo back, 6" lift on 37s
2017 Heartland Torque T29 - Sold.
Couple of Arctic Fox TCs - Sold

KnowNuthin
Explorer
Explorer
Grit dog wrote:


There are a few options, not entirely clear without seeing your sub panel, but seems the easiest and safest no brainer is get a 30-20A pigtail and not ever touch the hot side of the box.

This is the Load center I haveโ€ฆ

There are a couple vacant slots still available for future circuitsโ€ฆ howeverโ€ฆ itโ€™s currently 16 degrees outside with snow forecast for the next few daysโ€ฆ

Iโ€™m trying to make this a plug-and-play scenario for nowโ€ฆ a plug in 50a adapter and an extension cord makes my time away from a cozy fire much lessโ€ฆ
2005 2500HD D/A CC LB 4X4 being pushed by:
2016 Grand Design Reflection 303RLS
2007 Ural GearUp Arctic

ktmrfs
Explorer
Explorer
Bobbo wrote:
LittleBill wrote:
so do all you guys who have 15 amp circuits in your house, where your lamps are plugged in use a 1 amp circuit breaker to each individual lamp?

I was going to type this very thing on reaching the end of the thread. You beat me to it. Every one of my 1/2 amp (60 watt) lamps is plugged into a 15 amp outlet protected by a 20 amp breaker. Yes, I am risking the 18g wire shorting out and melting creating a fire hazard. I don't care.


the lamps are likely using a 14 or 16 ga wire, entirely capable of handling 15 or 20A for a short period of time if the lamp were to cause a short. A 12Ga extension cord is NOT capable of handling 50A for any length of time.
2011 Keystone Outback 295RE
2004 14' bikehauler with full living quarters
2015.5 Denali 4x4 CC/SB Duramax/Allison
2004.5 Silverado 4x4 CC/SB Duramax/Allison passed on to our Son!

ktmrfs
Explorer
Explorer
enblethen wrote:
The lite wire becomes a fuse if you use the 50 ampere's circuit. Failure in the heater could cause wire to melt down and create a fire situation.


EXACTLY!!! whole point is to make sure the wiring downstream of the breaker can handle the max breaker current in the case of a downstream fault. !!!!!
2011 Keystone Outback 295RE
2004 14' bikehauler with full living quarters
2015.5 Denali 4x4 CC/SB Duramax/Allison
2004.5 Silverado 4x4 CC/SB Duramax/Allison passed on to our Son!

Bobbo
Explorer II
Explorer II
LittleBill wrote:
so do all you guys who have 15 amp circuits in your house, where your lamps are plugged in use a 1 amp circuit breaker to each individual lamp?

I was going to type this very thing on reaching the end of the thread. You beat me to it. Every one of my 1/2 amp (60 watt) lamps is plugged into a 15 amp outlet protected by a 20 amp breaker. Yes, I am risking the 18g wire shorting out and melting creating a fire hazard. I don't care.
Bobbo and Lin
2017 F-150 XLT 4x4 SuperCab w/Max Tow Package 3.5l EcoBoost V6
2017 Airstream Flying Cloud 23FB