motc777 wrote:
OK about an hour ago, I decided to try Propane mode. I checked outside and sure enough, the burner fired right up. After one hour, I checked the pipe stack and the coils on the back. Both are warm. With the unit on electricity using the heating element, only the stack got warm, and never the coils on the back.
It's been close to 1.5 hours, and in the freezer, what little water drops have frozen.
I guess the real test ill be in the morning after it's run all night tonight. But, for the sake of argument, if this unit runs on propane, but will not work on electricity only (i.e. Auto) and reminding everyone I just put in a brand new element, what could it be?
Control board?
โNov-26-2018 05:12 PM
โNov-26-2018 04:55 PM
โNov-26-2018 03:07 PM
โNov-26-2018 01:22 PM
โNov-19-2018 04:40 AM
โNov-19-2018 03:57 AM
โNov-18-2018 06:27 PM
โNov-18-2018 06:07 PM
โNov-18-2018 06:06 PM
โNov-18-2018 05:43 PM
โNov-18-2018 03:29 PM
Old-Biscuit wrote:
Display panel lights, interior light etc....ALL 12V DC
Electric doesn't use the 'check light'---that is only a function of propane side
If you have fridge in AUTO it will select AC as priority
No AC available it will swap to 'gas'...if gas fails to light/prove 'Check' Light comes on
In AUTO and fridge remains on AC the AC power is available, AC Fuse on circuit board is good BUT electric element is bad cause no cooling is happening
OR the cooling unit has fail (blockage)
If thermistor/preset thermostat fail then fridge goes into LIMP Mode....CONTINUOUS cooling which will freeze both freezer and food compartment
Sounds more like the electric element has failed
325W element.....44 ohms....2.7A when energized
โNov-18-2018 03:27 PM
2oldman wrote:
You do not smell ammonia, but have you opened the back and looked? Are the coils warm/hot?