Dometic Penguin II A/c Heat pump installation

goldtop1
Explorer
Explorer
Hi all, well I just finished changing out the old Dometic heat pump for a new 15,000 BTU model. All went well till I powered it up. The T-stat has power and so does the unit. When it is powered up the heat pump comes on and stays on. It does not switch to A/C. It also will not turn off when the T-stat is off. Any help will be appreciated greatly. Also are there dip switches on the unit on the roof as well as in the power module? When I received the unit and accessories there were no installation instructions included.
7 REPLIES 7

goldtop1
Explorer
Explorer
All right with your help Doug I finally got it up and running. I took off the multizone module and wired it direct. I also found some installation instructions from a couple of years ago I guess. It showed the dip switches up stairs also and I found them and used the ones I need. So all is great now Thank you so much for all your help on this project. I just didn't know there was a control board upstairs.:) It all came with no instructions!

djedgar
Explorer
Explorer
Check this link for installation instructions:

http://www2.dometic.com/fe9ddc2e-b45b-4c88-9f1f-2d34e529d640.fodoc

or just do an Internet search, the diagrams and instructions may help you. It does explain how to set the dip switches (pg 18)
07 Newmar Ventana 3330
02 Honda Sabre
02 Kawa Vulcan Nomad
48 MG TC

dougrainer
Nomad
Nomad
goldtop1 wrote:
Hey Doug, I don't follow, there are 6 wires coming down from the top. 2 yellow , 2 blue a red and a black. Plus two phone jack wires. If what you say is correct, what do these wires hook to? The same six wires off the multi zone module are the same color so I wired them color to color. I plugged the phone jack in for the T-stat and of course hooked up the 12VDC to the red and black wires to the module. All I get is heat. The T-stat flashes E5 and the temp set.Help!


You have to REMOVE the original Module. That module is a 5 button module. Those 6 wires and the Phone type connectors come from the 12 button module mounted on the top area of the Penguin. Like I stated, you messed up big time. You will have to go on top and set the DIP switches on the module on top. Did the penguin NOT come with a 2 x 4 metal box with the 120 wires in it? Doug

goldtop1
Explorer
Explorer
Hey Doug, I don't follow, there are 6 wires coming down from the top. 2 yellow , 2 blue a red and a black. Plus two phone jack wires. If what you say is correct, what do these wires hook to? The same six wires off the multi zone module are the same color so I wired them color to color. I plugged the phone jack in for the T-stat and of course hooked up the 12VDC to the red and black wires to the module. All I get is heat. The T-stat flashes E5 and the temp set.Help!

dougrainer
Nomad
Nomad
Also are there dip switches on the unit on the roof as well as in the power module?

I missed that. Are you stating you have a 8 x 8 inch galvanized box with a control board? If so, that means you really messed up. The Penguins come with a 12 button control board up in the HP box accessed from the top. So, it appears you are trying to utilize 2 different control boxes, which is impossible to do and I have never heard or seen that happen. You have to remove the original control module. Doug

goldtop1
Explorer
Explorer
Hi Doug I also have the new CCC2 T-stat installed. I removed the older T-Stat because I knew it wouldn't communicate properly.So everything is new.

dougrainer
Nomad
Nomad
1. You still have the 5 button wall CCC tstat control?
2. IF SO, did you install the 12 button to 5 button control board on the new Penguin?
3. IF yes to question 1 and NO to question 2, That is your problem.
4. IF yes, to question 2, you did not install and wire the 12 to 5 button board correctly. Doug