โAug-23-2023 04:01 PM
โSep-19-2023 04:26 PM
Bud
USAF Retired
Pace Arrow
โSep-19-2023 03:28 PM
ScandentTrek wrote:
Update! I ordered and installed a new converter and it seems to have completely solved our problem. Also, it's much quieter and doesn't run nearly as hot, with much less fan noise. Overall, the installation was simple, with most of the difficulty coming from wrangling the wires back into the spaces and getting the new breaker board on.
Thank you all for your advice and help, it's a relief to have a functioning electrical system that's humming along as it should.
โSep-19-2023 02:36 PM
โAug-25-2023 07:59 PM
enblethen wrote:
The converter that I link at Best Converter is only $219
Don't go cheap!
โAug-25-2023 07:57 PM
Bud
USAF Retired
Pace Arrow
โAug-25-2023 07:54 PM
enblethen wrote:
I hope you mean "17-volts" not amps!
120-volt 15 amp should not have any effect as long it is good solid 120-volts.
Did you read voltage output with battery disconnected?
Did you call Best Converter for their input?
โAug-25-2023 02:53 PM
โAug-25-2023 12:08 PM
Bud
USAF Retired
Pace Arrow
โAug-25-2023 11:56 AM
โAug-24-2023 07:10 AM
ScandentTrek wrote:MFL wrote:bgum wrote:
I can't figure out how you're doing all that on 15 amps. That circuit is over loaded.
^This...running the AC alone on a 15A circuit, would be a heavy load. Any additional electrical load should trip the breaker. The converter charger is likely overloading, so helps to shut it off.
To be there that long, a 30 amp circuit, with 10/2 minimum wire would be a wise investment. I used 8/2 to run 75'.
Jerry
We haven't had an issue with the breakers tripping. Our AC unit is as old as the trailer and fairly small.
How would using too much AC power (not enough to trip the breaker) cause the converter charger to overload? I would think the breakers (in the house or in the trailer) would trip first before any kind of overload could occur.
โAug-24-2023 06:07 AM
Bud
USAF Retired
Pace Arrow
โAug-24-2023 06:01 AM
โAug-23-2023 06:38 PM
โAug-23-2023 06:25 PM