HELP!!!!!! with last step of inverter install

mdock2
Explorer
Explorer
I'm finishing up on installing the AIMS Power PWRIX120012S 1200 Watt Pure Sine Inverter, with Built In Transfer Switch. i have installed a sub panel, and should the sub panel be Bonded or not.

Thanks for your help...
marty
Marty (KI4NAI)& Shirley
1998,38' DutchStar F/L Cat

MEMBERSHIPS
FMCA
Bits & Bytes,
Elks International (Webmaster)
FCCC
PPA (Life Member)
Moose
ARRL-ARES
National Park Travelers Club
Visited 158 National Parks
Places we've slept since 2007
22 REPLIES 22

2oldman
Explorer II
Explorer II
beemerphile1 wrote:
I'm curious why you need a subpanel?
x2. That's a big job for not being able to remember what not to run off inverter.
"If I'm wearing long pants, I'm too far north" - 2oldman

beemerphile1
Explorer
Explorer
I'm curious why you need a subpanel? It is only 1200 watts which is equivalent to 10 amps.
Build a life you don't need a vacation from.

2016 Silverado 3500HD DRW D/A 4x4
2018 Keystone Cougar 26RBS
2006 Weekend Warrior FK1900

wa8yxm
Explorer III
Explorer III
Sub panels are **NEVER** Bonded. in fact that is the difference between a SUB panel and a MAIN panel. NOTE the "Main" panel in a motor home is really a SUB panel

Now depending on the inverter you may set it to bond when in inverter mode.

But you do not bond the panels. EVER in an RV. Just the inverter and the generator get bonded. At the inverter and at the generator.

Shore power is bonded at the shore (Park end of things).
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

mdock2
Explorer
Explorer
Ok, thanks all, that was the only issue holding me up on finish up the install. So sub panel is NOT to be bonded. The inverter is grounded to the frame, the metal sub panel case is grounded to the main panel using 3 wire romex....

marty
Marty (KI4NAI)& Shirley
1998,38' DutchStar F/L Cat

MEMBERSHIPS
FMCA
Bits & Bytes,
Elks International (Webmaster)
FCCC
PPA (Life Member)
Moose
ARRL-ARES
National Park Travelers Club
Visited 158 National Parks
Places we've slept since 2007

time2roll
Nomad
Nomad
No neutral-ground bond anywhere in the RV and not in the new subpanel either.

Only bond should be at the power source such as the main utility panel(not your RV panel). If the inverter internally bonds the neutral-ground as part of normal operation that is OK.

All grounds need to be connected and to the RV frame also. This includes the inverter chassis and the metal subpanel case if applicable.

mdock2
Explorer
Explorer
ok, i'm hardwiring inverter to sub panel then to circuits that i want to operate in rv from inverter when shore power/gen set is off. The inverter has a transfer switch that gets the power from the main panel and if line is hot, the inverter cuts off
Marty (KI4NAI)& Shirley
1998,38' DutchStar F/L Cat

MEMBERSHIPS
FMCA
Bits & Bytes,
Elks International (Webmaster)
FCCC
PPA (Life Member)
Moose
ARRL-ARES
National Park Travelers Club
Visited 158 National Parks
Places we've slept since 2007

BFL13
Explorer II
Explorer II
What exactly do you mean by "bonded" ? In Rvs the main dist panel for the 120v breakers is not bonded. The shore power source panel the pedestal receptacles are on is the bonded one.

So your sub-panel from the inverter needs to be carefully defined as to what you are doing.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

larry_cad
Explorer II
Explorer II
"boned"???

Or did you mean "bonded"??

If you mean bonded, then the answer is no!! NEC specifies a "sub panel" is to have isolated neutral bus bar, carried back to the main panel.