CoachFiver wrote:
But we are still either vapor locking or control board is getting too hot and shutting off fuel flow.
โJul-29-2019 10:35 AM
โJul-27-2019 05:32 PM
โJul-27-2019 05:23 PM
wopachop wrote:
What a bummer man. You spent a couple thousand at cw and an Onan technician came out twice?
I wonder if there is paper work documenting his Hot Air Recirculation Test? If not maybe you can recoup some dinero.
โJul-27-2019 04:33 PM
โJul-24-2019 09:40 AM
โJul-24-2019 06:05 AM
โJul-24-2019 04:39 AM
CoachFiver wrote:
If I run my generator with compartment door shut it will shut down in 70 degree weather. There is just not enough of a baffle separating the exhaust side air and the intake side air. Going to try my homemade sheet metal heat deflector this weekend.
โJul-23-2019 03:26 PM
โJul-23-2019 12:53 PM
โJul-23-2019 12:23 PM
โJul-23-2019 11:50 AM
โJul-23-2019 11:36 AM
shastagary wrote:
from the installation manualHot Air Recirculation Test A representative installation of the genset must be tested to determine that the genset will not overheat due to recirculation of hot air back into the genset.
8.4 Test Requirement The rise in inlet air temperature over ambient air temperature must not exceed 15ยฐF (8ยฐC). A rise in inlet air temperature indicates hot air recirculation. If the rise exceeds the requirement,steps must be taken to reduce recirculation to an acceptable level.