Tom/Barb wrote:ScottG wrote:
That's not the case. It trips all the GFCI's at the facility but is ok on a standard 30A (no GFCI).
We do not know all the GFIs at the storage facility are good. they are probably all on the same circuit. and wired wrong.
a cheap tester will eliminate the doubt.
to determine if it is the trailer, simply read continuity between the two hot leads and the common ground on the trailer plug, it should show and open.
If it doesn't show an open circuit, it would pop the 30 amp breaker at home or smoke something.
.
Jan-06-2018 08:29 PM
Tom/Barb wrote:
...It is easy to determine if it is the trailer. read continuity between the two hot legs and the Common ground of the plug, it should be open to both.
Jan-06-2018 08:27 PM
ktmrfs wrote:
open ground will NOT trip a GFI. A GFI is designed to work with a circuit that is not grounded, e.g. the old two prong plug.
there are TWO things that will cause a GFI to trip.
1) unbalanced current between the hot and neutral.
2) ground neutral short. e.g. somewhere downstream the ground and neutral are touching.
now a regular 30A RV circuit most often does NOT have a GFI, so no issue.
couple of things that could be causing an issue.
1) leakage in the fridge 120V element to ground.
one way to check is to turn OFF every breaker in the RV. GFI should Not trip. if it does, the fault is before the 30A main breaker. If no GFI trip, trip each circuit and see which one trips the GFI. whatever circuit trips the GFI tells you which circuit either has excessive leakage current or a ground neutral short.
Jan-06-2018 08:22 PM
ScottG wrote:
That's not the case. It trips all the GFCI's at the facility but is ok on a standard 30A (no GFCI).
Jan-06-2018 08:14 PM
Tom/Barb wrote:
No, it would not because a GFCI fault is not an overload.
Jan-06-2018 08:12 PM
ScottG wrote:Tom/Barb wrote:ScottG wrote:
Of course you have an open ground. Your ground isn't supposed to be bonded and none of that matters anyway. A GFCI doesn't trip because of an "open ground".
Somewhere, you have a leakage to ground. Could be a wet outside receptacle, bad fridge heater *even if it works fine) or water heater or even a bad microwave (rare). I would unplug the appliances and see if the fault remains.
If that was his problem, plugging it at home would pop the breaker.
No, it would not because a GFCI fault is not an overload.
OP, another thing that can cause it is a failing converter. I would turn off its breaker and see if it still trips the GFCI.
Jan-06-2018 08:11 PM
Tom/Barb wrote:ScottG wrote:
Of course you have an open ground. Your ground isn't supposed to be bonded and none of that matters anyway. A GFCI doesn't trip because of an "open ground".
Somewhere, you have a leakage to ground. Could be a wet outside receptacle, bad fridge heater *even if it works fine) or water heater or even a bad microwave (rare). I would unplug the appliances and see if the fault remains.
If that was his problem, plugging it at home would pop the breaker.
Jan-06-2018 08:10 PM
Jan-06-2018 08:09 PM
DBECHEN wrote:
Hi all, I have been having a problem with plugging into the shore power at our storage facility. They have all circuits run through GFCI outlets on the pole. When we plug in and we are not running anything the GFCI trips on the pole. We talked to our storage facility manager and they had an electrician come out and he said the issue was our RV having an open ground. We have a Progressive Industries surge protector that was installed by the first owner. When we plug into the 30 amp plug at our house and in campgrounds there is no problem. Any ideas what may be causing this? Thanks in advance.
Jan-06-2018 08:07 PM
Tom/Barb wrote:Tom/Barb wrote:
If it works every where but there, I would suspect there.
there is a cheap little tester for GFI circuits get one and test the storage facility.
It depends upon if the facility is using the white wire as a common ground or if they are using the bare copper to a ground post as the common ground.
TESTER
Jan-06-2018 08:05 PM
Tom/Barb wrote:
If it works every where but there, I would suspect there.
there is a cheap little tester for GFI circuits get one and test the storage facility.
It depends upon if the facility is using the white wire as a common ground or if they are using the bare copper to a ground post as the common ground.
TESTER
Jan-06-2018 08:03 PM
Tom/Barb wrote:ScottG wrote:
Of course you have an open ground. Your ground isn't supposed to be bonded and none of that matters anyway. A GFCI doesn't trip because of an "open ground".
Somewhere, you have a leakage to ground. Could be a wet outside receptacle, bad fridge heater *even if it works fine) or water heater or even a bad microwave (rare). I would unplug the appliances and see if the fault remains.
If that was his problem, plugging it at home would pop the breaker.
Jan-06-2018 08:02 PM
Tom/Barb wrote:
If it works every where but there, I would suspect there.
Jan-06-2018 08:01 PM
ScottG wrote:
Of course you have an open ground. Your ground isn't supposed to be bonded and none of that matters anyway. A GFCI doesn't trip because of an "open ground".
Somewhere, you have a leakage to ground. Could be a wet outside receptacle, bad fridge heater *even if it works fine) or water heater or even a bad microwave (rare). I would unplug the appliances and see if the fault remains.