pianotuna wrote:
Thanks for the numbers.
Apr-01-2019 06:14 PM
Apr-01-2019 06:04 PM
MrWizard wrote:
hope your luck is just as good, when the weather gets hotter
Apr-01-2019 04:46 PM
Apr-01-2019 04:24 PM
Apr-01-2019 09:42 AM
Apr-01-2019 07:44 AM
pianotuna wrote:
Here is a summary of 3 tons results.
2200 inverter genny in eco-->RV with prosine off-->air conditioner won't start
2200 inverter genny in eco-->RV with prosine on-->air conditioner won't transfer from prosine unless the genny is switched to full speed.
2200 inverter genny in eco-->autoformer-->RV with prosine on--air conditioner moves smoothing to genny, after starting on prosine.
--
Mar-31-2019 09:08 PM
Mar-31-2019 01:59 PM
Mar-31-2019 12:55 PM
Mar-31-2019 11:33 AM
Mar-31-2019 10:54 AM
MrWizard wrote:
An autoformer
Does NOT offer surge (sudden high voltage) protection
It DOES give some "voltage lag" protection
Where voltage drops under heavy startup loads
This is what the op is seeing, the autoformer boost/surges the voltage,
So there is less voltage drop/lag
That is NOT surge protection
That is low voltage protection