Goodson Engineering wrote:
The first (and most common) misconception is that a breaker trips when its nameplate rating is exceeded. One fire text has stated (incorrectly) that a circuit breaker will trip in several minutes with a small increase in current over its rating[1]. Actually, a 20 amp breaker must trip at a sustained current of 27 amperes (135 percent) at less than one hour, and at 40 amperes (200 percent of wire rating) in less than 120 seconds—far different from what the cited text implies. These two trip points (135 percent and 200 percent) are defined in NEMA Standard AB-1, MCCBs and Molded Case Switches[2]