otrfun wrote:StirCrazy wrote:You didn't state the model number. I would assume that's for the Renogy low-frequency 2000 watt inverter which costs about $600 and weighs about 50 lbs., right? That toroidal coil, which helps provide all the inrush current, makes for a heavy unit. Specs for most of these 2000 watt low-frequency inverters are somewhat similar in terms of their power/duration specs.
ok so here are the specs. once again renogy customer service was quick and efficient. so there is two specs one for max power (4000watts) and one for overload protection. so it will handle the max power (4000watts) for 5 seconds and if it hits a overload conditions that will trip the inverter to protect it with in 40milli seconds.
The high-frequency Renogy 2000 watt inverter, which costs about $300 and weighs 12 lbs. only has a 4000 watt peak rating as far as I can tell. My guess, the peak rating means it will only output 4000 watts for 20-40 milliseconds. Not enough time to produce much inrush current. I believe this is the unit the OP was looking at purchasing.
The Xantrex 2000 watt Freedom X inverter, which I believe is also a high-frequency unit (at 15 lbs.), will output 4000 watts >2 sec. Xantrex states specifically it's very effective for starting motors. That's an awesome spec for a high-frequency inverter.
Feb-01-2023 07:22 AM
Feb-01-2023 06:27 AM
StirCrazy wrote:You didn't state the model number. I would assume that's for the Renogy low-frequency 2000 watt inverter which costs about $600 and weighs about 50 lbs., right? That toroidal coil, which helps provide all the inrush current, makes for a heavy unit. Specs for most of these 2000 watt low-frequency inverters are somewhat similar in terms of their power/duration specs.
ok so here are the specs. once again renogy customer service was quick and efficient. so there is two specs one for max power (4000watts) and one for overload protection. so it will handle the max power (4000watts) for 5 seconds and if it hits a overload conditions that will trip the inverter to protect it with in 40milli seconds.
Feb-01-2023 05:45 AM
otrfun wrote:theoldwizard1 wrote:Sorry, have to respectfully disagree. One cannot be any "worse" or better than the other since they both, more or less, describe the same thing.
On refrigeration equipment you might find "locked rotor amperage" (LRA) which would be worse than normal inrush current.
Air conditioner manufacturers use LRA to quantify the inrush current drawn by the compressor motor at its rated voltage when the rotor is kept stationary. Or, put another way, LRA quantifies the inrush current necessary to place a stationary or locked rotor in a compressor motor in motion.theoldwizard1 wrote:Agree, it's not very common for manufacturers to use the term inrush current when providing specs for their products. The primary reason is because inrush current is a general descriptor for a short, momentary burst (or inrush) of current. The time/duration for measuring inrush current can vary for RV a/c compressors and small household motors as opposed to large commercial equipment.
No manufacturer specs their in rush current.
Inrush current, in terms of starting RV a/c compressors and smaller consumer-type AC motors, is typically measured in less than a second. A Fluke or Amprobe inrush current capable clamp-on ammeter bears this out because it provides inrush current results in less than second. The time/duration for the inrush current analysis is less than a second, but obviously much longer than what's required for a peak reading.
With that being said . . . if an inverter or inverter generator manufacturer specifies current and time/duration at multiple power levels, one can use this data to approximate inrush current performance. For example, a 2000 watt inverter (with a 2000 watt "continuous" power rating) that also has a 4000 watt *peak* power rating will probably provide minimal inrush current. A 2000 watt inverter that can also output 4000 watts for 1-2 seconds should provide excellent inrush current. A 2000 watt inverter that is capable of producing 4000 watts for 5-10 seconds (and/or 6000 watts for 1-2 seconds) should provide outstanding inrush current.
Hope this helps.
Jan-31-2023 09:40 AM
pianotuna wrote:I believe you're talking about the current encountered on the INPUT of the inverter when it's connected to a power source without first precharging the inverter caps with a resistor.
I can tell you that inrush on a 1000 watt psw inverter is high enough to blow a 30 amp fuse. And that is with no load. DAMHIK
Jan-31-2023 09:15 AM
theoldwizard1 wrote:Sorry, have to respectfully disagree. One cannot be any "worse" or better than the other since they both, more or less, describe the same thing.
On refrigeration equipment you might find "locked rotor amperage" (LRA) which would be worse than normal inrush current.
theoldwizard1 wrote:Agree, it's not very common for manufacturers to use the term inrush current when providing specs for their products. The primary reason is because inrush current is a general descriptor for a short, momentary burst (or inrush) of current. The time/duration for measuring inrush current can vary for RV a/c compressors and small household motors as opposed to large commercial equipment.
No manufacturer specs their in rush current.
Jan-31-2023 06:00 AM
StirCrazy wrote:otrfun wrote:StirCrazy wrote:You mentioned the Renogy 2000w PSW inverter. Very popular unit. Always wondered what time/duration they used for their peak rating. Did you happen to get this info?otrfun wrote:I do agree the lack of companies putting this in there advertising makes things a little more difficult. personaly I have never been met with any issues when I email the company and ask for that information.
IMO the most important takeaway when discussing inrush, starting, peak, or surge, current is the following: unless a specific time or duration (or testing standard/protocol) is specified for any given current rating, the current rating provides little insight into how the device will perform in the realworld.
not yet. I was actualy going to email them and see after what you said the other day. hang on I'll email them now and let you know. I have a go power 2000watt inverter in the 5th wheel and it has never had an issue running anything. I think it actualy started my ac once by accident haha.. but I am looking at the renogy for the camper.
Steve
Jan-31-2023 05:58 AM
otrfun wrote:StirCrazy wrote:You mentioned the Renogy 2000w PSW inverter. Very popular unit. Always wondered what time/duration they used for their peak rating. Did you happen to get this info?otrfun wrote:I do agree the lack of companies putting this in there advertising makes things a little more difficult. personaly I have never been met with any issues when I email the company and ask for that information.
IMO the most important takeaway when discussing inrush, starting, peak, or surge, current is the following: unless a specific time or duration (or testing standard/protocol) is specified for any given current rating, the current rating provides little insight into how the device will perform in the realworld.
Jan-30-2023 02:16 PM
Jan-30-2023 01:39 PM
Jan-30-2023 01:31 PM
LaneW wrote:
You folks are very helpful, thanks. I do get it about wiring and will plan to discard what comes with an inverter and oversize the cabling.
LaneW wrote:
But how do I find out about the inrush current matter? That's a bit concerning to me. I want to do all of this once only and get it right the first time.
Jan-30-2023 07:05 AM
otrfun wrote:StirCrazy wrote:You mentioned the Renogy 2000w PSW inverter. Very popular unit. Always wondered what time/duration they used for their peak rating. Did you happen to get this info?otrfun wrote:I do agree the lack of companies putting this in there advertising makes things a little more difficult. personaly I have never been met with any issues when I email the company and ask for that information.
IMO the most important takeaway when discussing inrush, starting, peak, or surge, current is the following: unless a specific time or duration (or testing standard/protocol) is specified for any given current rating, the current rating provides little insight into how the device will perform in the realworld.
Jan-30-2023 06:55 AM
StirCrazy wrote:You mentioned the Renogy 2000w PSW inverter. Very popular unit. Always wondered what time/duration they used for their peak rating. Did you happen to get this info?otrfun wrote:I do agree the lack of companies putting this in there advertising makes things a little more difficult. personaly I have never been met with any issues when I email the company and ask for that information.
IMO the most important takeaway when discussing inrush, starting, peak, or surge, current is the following: unless a specific time or duration (or testing standard/protocol) is specified for any given current rating, the current rating provides little insight into how the device will perform in the realworld.
Jan-30-2023 06:20 AM
otrfun wrote:
IMO the most important takeaway when discussing inrush, starting, peak, or surge, current is the following: unless a specific time or duration (or testing standard/protocol) is specified for any given current rating, the current rating provides little insight into how the device will perform in the realworld.
Jan-29-2023 12:16 PM
StirCrazy wrote:IMO starting current is just a colloquial term to sometimes describe inrush current and not related to any particular type of equipment. Also, peak current is very different from inrush current (see last paragraph).otrfun wrote:inrush and starting current are the same, just different names depending on the type of equipment. in rush covers any time a electric componant temporatly draws more power when you turn it on, in a motor it is generaly called starting current. every inverter I have seen lists this as peak power. and its usaly a couple K watts above the rated output. for example the renogy is a 2000 watt inverter continious with a peak of 4000 watts that will handle anything on a rv but maby not two large power users at once.
. . . Choosing a capable 2000w inverter is important. Not all 2000w inverters are created equal. Although most inverters can supply their continuous current rating, many fall short providing suitable amounts of inrush current. Inrush current is necessary to successfully start a/c units and microwaves. Unfortunately, very few manufacturers provide inrush current specs for their inverters.
Good luck!
Steve