clipper1014 wrote:
Thanks I have a WFCO model WF-8735P. The heater is on the same line as the bath,bed,slide(I don't have a slideout) & lights. Where do you suggest conecting to?
โNov-03-2017 02:52 PM
โNov-03-2017 02:26 PM
Old-Biscuit wrote:SO is this the CORRECT answer?!?!? :B
High AC Ripple will cause DC circuit board failures
Unfiltered DC will cause circuit board failures
All of the individual DC fused circuits are NOT necessarily 'filtered'.
Lighting circuits do not NEED to be fed from a filtered circuit.
I suspect that is your problem.
What is the Brand/Model of your converter?