Not sure if this response was directed at me... but anyway to clarify, I never have (or ever intend to) hookup from the generator into my house directly. I simply run a cable from the gen, and hookup the devices (usually 3-4 critical appliances) ...
Thanks for clarifying. Exact same issue I have experienced. Professor95 in this thread says it is not the Voltage Regulator at fault.. may be true... either way, I have found no way to reliably use the 240V outlet to power household appliances sa...
Say more. Does this mean that you too experience extreme voltage drops when using the 240V to power 120V loads? Not sure what you mean by 'unbalanced', but I think you experienced the same issue that I have in the past in the same configuration. ...
Thank you professor, very helpful post. I did swap the loads when I conducted the test, and the problem was gone. I was planning on using the cord with only one side loaded because of this issue, but that defeats the purpose of obtaining full 30AM...
I conducted those earlier tests using a Kill-A-Watt. The load tested consisted of a sump pump which peaks at ~1500 W upon start. The only other loads tested were smaller 100W lamps etc.I looked at the circuit diagram again. In my opinion the AVR o...