Jun-03-2014 04:09 PM
Jul-06-2014 12:15 AM
Golden_HVAC wrote:
As a general rule, yes you must have at least the minimum voltage rating of the replacement capacitor as the expected running voltage in the system. So a 120 volt compressor will see upwards of 175 volts at it's run capacitor, thus the minimum rating of 370 volts.
That said, a start capacitor with relay to take that compressor out of the circuit once the compressor is running must be properly sized. Oversize it and the correct "Drop out" voltage will not be obtained in time or at all. So a start relay that works great on a 220 volt compressor and drops out the capacitor at 190 volts on the start to run winding will work great with 200 - 250 volts input to the compressor. However move it to a 120 volt compressor, and it will never drop out, unless it has a back up timer circuit to take the start capacitor out of the circuit after a certain time has gone by. The SPP6E does have a electronic timer, and anyone putting this 220 volt capacitor on a 120 volt circuit is doing so hoping that the timer keeps working. The capacitor has a maximum working volt rating around 300 - 370 volts, so that is not a problem, the problem is the minimum voltage to drop out the start capacitor is well above what a 120 volt compressor will run at.
The SPP4E is the correct start capacitor for a 120 volt compressor, and will drop out at the correct voltage, even if the time circuit fails.
Jun-15-2014 09:57 AM
Beyer wrote:
I have a 1996 camper with a Coleman A/C. I bought the Supco SPP6E. My A/C has 2 round capacitors, one small and one large. The small one has 2 wires and the large has 3 wires. Which one do I replace? Both?
Pics:
http://i1372.photobucket.com/albums/ag321/beyer25/Mobile%20Uploads/image_zpsf3f66b5c.jpg
wwest wrote:like2rok wrote:
When i start it cold, then go to Eco Mode On, then RPM's are slightly higher than when it warms up and slows down even more. It IS Much Slower than Eco Off which wastes fuel overnight when the AC only needs to run a few minutes per hour. On this thread Please Refrain from suggesting the easy fix of Eco Off.
The entire purpose of spending $1000+ on this Inverter Generator is the Fuel Economy/quiet operation and I refuse to settle with Eco Off as a solution.
I will keep this thread updated on the attempts to modify eco idle speed or rejetting.
FYI I have the Whynter GREEN ARC-110WD AC with dual hoses that specs state 9.5amps maximum current
Simple. You need to add a TDR, Time Delay Relay, and a heavy electrical load (***)to your A/C.
The idea is that the relay delays providing power to the compressor for 2-3 seconds, initially providing a connection to the new "load". A/C switch "demands" cooling, the load comes on line, the genset revs up to speed, then the TDR switches the AC to the compressor.
*** 2 500W halogen bulbs.
An AC typically draws 3X the running load at compressor startup, maybe even 5X at times, high head pressure.
Jun-15-2014 09:00 AM
Jun-15-2014 03:12 AM
ScottG wrote:
General rule for capacitors; voltage rating of a cap is not important as long as it is greater than what your using it for. It's like having a higher rated wire insulation.
In this case the voltage rating has no impact on the operation of the capacitor and its circuit.
It's the capacitance value that is critical.
Porsche or Country Coach!
If there's a WILL, I want to be in it!
Jun-15-2014 03:02 AM
Porsche or Country Coach!
If there's a WILL, I want to be in it!
Jun-06-2014 04:51 AM
Chris Bryant wrote:Beyer wrote:
So, if I replace both of my capacitors (start and run) with the new Supco, how should the wiring look on that?
The Supco has 2 wires and the old "large" capacitor has 3 wires and the "small" capacitor has 2 wires.
It should piggyback off the large capacitor- it will not replace anything.
Just to be clear- the large capacitor has 3 wires, but only 2 actual connections, just a couple of wires to the same connection. This is a separate compressor and fan capacitor, most now use a single combo capacitor which has "herm" "Fan" and "Com" terminals.
Jun-04-2014 07:25 PM
Beyer wrote:
So, if I replace both of my capacitors (start and run) with the new Supco, how should the wiring look on that?
The Supco has 2 wires and the old "large" capacitor has 3 wires and the "small" capacitor has 2 wires.
Jun-04-2014 03:57 PM
Beyer wrote:
So, if I replace both of my capacitors (start and run) with the new Supco, how should the wiring look on that?
The Supco has 2 wires and the old "large" capacitor has 3 wires and the "small" capacitor has 2 wires.
Jun-04-2014 02:57 PM
Jun-04-2014 01:38 PM
Dutch_12078 wrote:
The SPP6E works fine on my Dometic/Duo-Therm 13.5 A/C's. The capacitance of the SPP4E and the SPP6E are the same, and I went with the recommendations of RV Tech Chris Bryant in choosing the 6E's. The packages I bought show the voltage rating as "90-277VAC". On my A/C's, the smaller round black capacitor is the compressor start capacitor in series with a Cera-Mite PTCR. Both were replaced by the SPP6E. The larger three terminal capacitor is the run cap for both the compressor and fan motors. My Honeywell digital thermostats prevent "instant" A/C restarts anyway, so that's not an issue.
Jun-04-2014 08:50 AM
Jun-04-2014 07:01 AM
Dutch_12078 wrote:
The SPP6E works fine on my Dometic/Duo-Therm 13.5 A/C's. The capacitance of the SPP4E and the SPP6E are the same, and I went with the recommendations of RV Tech Chris Bryant in choosing the 6E's. The packages I bought show the voltage rating as "90-277VAC". On my A/C's, the smaller round black capacitor is the compressor start capacitor in series with a Cera-Mite PTCR. Both were replaced by the SPP6E. The larger three terminal capacitor is the run cap for both the compressor and fan motors. My Honeywell digital thermostats prevent "instant" A/C restarts anyway, so that's not an issue.
Jun-04-2014 06:04 AM
Jun-04-2014 02:42 AM
Porsche or Country Coach!
If there's a WILL, I want to be in it!