Trail-Mate wrote:
If a 30 amp only pedestal (not 50 amp) 30 amp is the max load for the entire pedestal the 30 amp plug and the 20 amp.
Jan-02-2014 06:14 AM
j2catfish wrote:X-3 and the 80% is for any size breaker even super big ones in industrial use.
X2 - finally someone has stated the design (correct) amp draw. Always plan for the 80% and you will probably have no problems with circuit breakers popping. If this is not sufficient, about the only real solution is to re-engineer the main power to the coach for 50 amp service.
Just my take, your opinion may vary but check with a good/experienced electrician.
Catfishpianotuna wrote:
Hi,
The continuous duty is 80% of 30 amps. i.e. you really only have 24 amps available for constant use.
The fridge draws more like 4 amps not ten.
For brief periods of time (read a second or two) drawing more than what the breaker is rated at will rather rarely trip it.
Jan-02-2014 05:02 AM
Jan-02-2014 04:17 AM
Jan-02-2014 03:48 AM
Jan-02-2014 02:46 AM
Jan-01-2014 07:21 PM
pianotuna wrote:
Hi,
The continuous duty is 80% of 30 amps. i.e. you really only have 24 amps available for constant use.
The fridge draws more like 4 amps not ten.
For brief periods of time (read a second or two) drawing more than what the breaker is rated at will rather rarely trip it.