I think I may know the answer to this, but just want to help educate myself in case I don't quite understand.

If you are plugged into a 30 amp power source - does that mean you cannot draw more than 30 amps without tripping a breaker?

So, let's say I have a fireplace going which draws 11.7 amps max, the refrigerator which let's say draws 10 amps, and a microwave going that draws 9 amps - then I am at my limit on amps from a 30 amp plug?
Charlie & Jeri
2013 Keystone Cougar 327RES
2013 Dodge Ram 3500 EC
14 REPLIES 14

pianotuna
Nomad III
Nomad III
Hi Tom,

There is an improper way to modify a pedestal using the wires for energizing both the 30 amp and 20 amp outlets. In that case, it is possible to overload the feed line coming to the pedestal and the breakers would not trip.


I know it is illegal to wire in this manner where I live--so the scenario of an overloaded pedestal is not going to happen, when I'm in a campground within Saskatchewan.
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

wildtoad
Explorer II
Explorer II
Trail-Mate wrote:
If a 30 amp only pedestal (not 50 amp) 30 amp is the max load for the entire pedestal the 30 amp plug and the 20 amp.


Is this true even if they have their own breaker??
Tom Wilds
Blythewood, SC
2016 Newmar Baystar Sport 3004
2015 Jeep Wrangler 2dr HT

john_bet
Explorer II
Explorer II
j2catfish wrote:
X2 - finally someone has stated the design (correct) amp draw. Always plan for the 80% and you will probably have no problems with circuit breakers popping. If this is not sufficient, about the only real solution is to re-engineer the main power to the coach for 50 amp service.
Just my take, your opinion may vary but check with a good/experienced electrician.
Catfish


pianotuna wrote:
Hi,

The continuous duty is 80% of 30 amps. i.e. you really only have 24 amps available for constant use.

The fridge draws more like 4 amps not ten.

For brief periods of time (read a second or two) drawing more than what the breaker is rated at will rather rarely trip it.
X-3 and the 80% is for any size breaker even super big ones in industrial use.
2018 Ram 3500 SRW CC LB 6.7L Cummins Auto 3.42 gears
2018 Grand Design 337RLS

Gooselover
Explorer
Explorer
Thanks everyone for clarifying this for me! I guess my thinking pattern was correct!
Charlie & Jeri
2013 Keystone Cougar 327RES
2013 Dodge Ram 3500 EC

Veebyes
Explorer II
Explorer II
Pretty easy to tell if you are at overload or very close to it. Go out & feel the power cord at the plug & feel the circuit breaker. If they are warm or hot turn something that draws big power off. Start with things that create heat such as the water heater, the hair drier, the coffee maker, toaster, you get the idea.
Boat: 32' 1996 Albin 32+2, single Cummins 315hp
40+ night per year overnighter

2007 Alpenlite 34RLR
2006 Chevy 3500 LT, CC,LB 6.6L Diesel

Ham Radio: VP9KL, IRLP node 7995

Trail-Mate
Explorer
Explorer
You can overheat the pedestal . Plug into 30 amp and run it close or at max power for the 30, then plug in a 1500 watt heater in the 20 amp plug in the same pedestal. None of the breakers will trip but you can overheat the pedestal and could cause a fire. If a 30 amp only pedestal (not 50 amp) 30 amp is the max load for the entire pedestal the 30 amp plug and the 20 amp. I encountered this last year when I was on a 30 amp just getting set for winter. The pedestal got very hot and could smell wiring. Breakers would not trip because each one was not over the limit for their load, but together it was overloaded. From my encounter with this. on a 30 amp pedestal, I would run a 1500 watt electric from inside the camper( 30 amp ) and no more that a 750 watt on the extension cord to 20 amp outlets.
1997 Ford F250 Extended Cab, 7.3 Diesel, 8 foot bed.
Reese 16K Hitch
(Moved into Shed) Hensley Arrow
Jordan Brake Controller, Hensley TruControl Gold Shelved.
Open Range 5th Wheel, Roamer RF392 BHS


Happy Camping !!

RoyB
Explorer II
Explorer II
We like to use a couple of electric heaters verses the propane furnace and most of the time can run an separate extension cord out to the CG pedestal and plug into their 20AMP service plug just for the electric heaters. This has its own circuit breaker and does not take away from the 30AMP circuit breaker.

Roy Ken
My Posts are IMHO based on my experiences - Words in CAPS does not mean I am shouting
Roy - Carolyn
RETIRED DOAF/DON/DOD/CONTR RADIO TECH (42yrs)
K9PHT (Since 1957) 146.52M
2010 F150, 5.4,3:73 Gears,SCab
2008 Starcraft 14RT EU2000i GEN
2005 Flagstaff 8528RESS

j2catfish
Explorer
Explorer
X2 - finally someone has stated the design (correct) amp draw. Always plan for the 80% and you will probably have no problems with circuit breakers popping. If this is not sufficient, about the only real solution is to re-engineer the main power to the coach for 50 amp service.
Just my take, your opinion may vary but check with a good/experienced electrician.
Catfish


pianotuna wrote:
Hi,

The continuous duty is 80% of 30 amps. i.e. you really only have 24 amps available for constant use.

The fridge draws more like 4 amps not ten.

For brief periods of time (read a second or two) drawing more than what the breaker is rated at will rather rarely trip it.
K3500; Teton Homes 5er;
Native Texan - Transplanted Tar Heel
Retired USMC Mustang (LDO)
Semper Fi !

pianotuna
Nomad III
Nomad III
Hi,

The continuous duty is 80% of 30 amps. i.e. you really only have 24 amps available for constant use.

The fridge draws more like 4 amps not ten.

For brief periods of time (read a second or two) drawing more than what the breaker is rated at will rather rarely trip it.
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

Golden_HVAC
Explorer
Explorer
Hi,

THe circuit breaker can go over it's limit for a short time if it is a small amount over the 30 amp limit. So it might hold exactly 30.2 amps all night long. Or trip at 31 amps after about 1 minute. Instant trip will happen at 45 amps or more, while it should trip within 3 seconds when between 35 and 45 amps.

Anyway if you want to make sure it will not trip, keep amperage below 25 amps, and you will not be overloading the circuit breaker or the wiring, and probably will not overheat the plug or receptacle. However I have overheated a bad receptacle at only 16 amps draw before, with a 13 volt drop across the receptacle at that point.

So basically keep track of the amperage of the items you plan to run, and you can keep it below 30 amps pretty easy.

Remember that the converter/charger will always be on unless you can turn it off. So it can use 1-2 amps most of the time, or up to 4 amps when the batteries are close to dead.

A TV set is about 1 amp, but the flat screens can be less.

Your refrigerator is only 3.5 amps - if it is a propane / electric one. Might be 3-5 amps if it is a 120 volt compressor type such as used at home, with an additional 3 amps during ice harvest.

Your electric heater can be 12.5 amps on high heat, but you can reduce that to about 8 amps on the low setting.

Electric water heaters can use between 3 and 8 amps, depending on model.

Electric blankets are about 1 amp.

What is surprising is toasters are 8-10 amps.

Hair Dryers up to 12.5 amps

Air conditioners can use 12 amps on a cooler day, and up to about 14 amps when it is over 100F outside. However their surge amperage when restarting can be 35 amps for about 3 seconds - that is why the 30 amp breakers do not trip at exactly 30 amps, but will hold at 55 amps for a couple of seconds.

Fred.
Money can't buy happiness but somehow it's more comfortable to cry in a

Porsche or Country Coach!



If there's a WILL, I want to be in it!



I havn't been everywhere, but it's on my list.

Kangen.com Alkaline water

Escapees.com

wandering1
Explorer
Explorer
Sounds like you need a calculator??????
HR

Yaj
Explorer
Explorer
You are actually .7 amps aver the breaker limit and it will probably trip. Breakers don't like to be operated at their limit.

newman_fulltime
Explorer II
Explorer II
Repeat this 30amps is 30amps no more you connot get more cheat it outsmart it it knows.