RustyJC wrote:
If the two hot legs are in phase as you describe, there's a real risk of overloading the neutral conductor in your shore power cord. Neutral leg current is the sum of the hot leg currents, but because "proper" 120/240VAC split phase center tap neutral 50A service has the two hot legs 180* out of phase, one leg is mathematically assigned a minus (-) sign. Thus, in a "proper" 50A setup, if both legs were drawing 50 amps, the neutral current would be 50 + (-50) = 0 amps. If it were wired in phase as you describe, then neutral leg current would be 50 + 50 = 100 amps; the neutral conductor is sized for 50 amps, so the potential problem is obvious.
Besides, most power management systems look for 240VAC across L1 and L2 as an indicator that 50A service is available. If they see 0VAC across L1 and L2, they default to 30A service - that's what my system does. By doing so, it prevents the overloaded neutral conductor situation described above.
Rusty
โJul-30-2015 06:48 AM
RustyJC wrote:
If the two hot legs are in phase as you describe, there's a real risk of overloading the neutral conductor in your shore power cord. Neutral leg current is the sum of the hot leg currents, but because "proper" 120/240VAC split phase center tap neutral 50A service has the two hot legs 180* out of phase, one leg is mathematically assigned a minus (-) sign. Thus, in a "proper" 50A setup, if both legs were drawing 50 amps, the neutral current would be 50 + (-50) = 0 amps. If it were wired in phase as you describe, then neutral leg current would be 50 + 50 = 100 amps; the neutral conductor is sized for 50 amps, so the potential problem is obvious.
Besides, most power management systems look for 240VAC across L1 and L2 as an indicator that 50A service is available. If they see 0VAC across L1 and L2, they default to 30A service - that's what my system does. By doing so, it prevents the overloaded neutral conductor situation described above.
Rusty
โJul-30-2015 02:32 AM
Sport45 wrote:taken wrote:
I had a hard time following how you messed up the adapter. However, to clarify, the 50 AMP cord that RV's with 50 AMP service use as well as it's corresponding outlet is indeed 220V. 220V comes into the RV as the two hot legs are on opposite phases.
50 AMP Service Explained.
That's probably the most-used configuration, but do the two 110 feeds have to be opposite legs? Seems it would work just as well if they came off the same bus. Might work even better as an open neutral condition couldn't put 220V across anything. Of course no 220V appliance in the RV would work...
โJul-29-2015 09:40 PM
taken wrote:
I had a hard time following how you messed up the adapter. However, to clarify, the 50 AMP cord that RV's with 50 AMP service use as well as it's corresponding outlet is indeed 220V. 220V comes into the RV as the two hot legs are on opposite phases.
50 AMP Service Explained.
โJul-29-2015 09:04 PM
โJul-29-2015 08:52 PM
taken wrote:
I had a hard time following how you messed up the adapter. However, to clarify, the 50 AMP cord that RV's with 50 AMP service use as well as it's corresponding outlet is indeed 220V. 220V comes into the RV as the two hot legs are on opposite phases. Just like in your home, they then feed opposite phases in your breaker box. Since all your breakers only tie into one or the other, they only get 110V. However, 220V absolutely does come into your RV.
Anyways, sorry about your mix up and glad it only got a couple of appliances as opposed to something bigger...
Oh, and here is a great site explaining RV 50 AMP 110/220V service...
***Link Removed***
โJul-29-2015 02:22 PM
โJul-29-2015 12:22 PM
2oldman wrote:
How are your ears after listening to that generator?
โJul-29-2015 10:49 AM
MNRon wrote:
What tommy said!!!
Some of responses don't know any more than the OP, other than they know enough not to make this mistake.
โJul-29-2015 10:09 AM
โJul-29-2015 07:43 AM
byrdr1 wrote:RustyJC wrote:
The repair bill for our daughter and son-in-law's 5th wheel was $7500+ due to a dropped neutral in the RV's power cord that applied 240VAC to all of the 120VAC loads. They had power protection, but it plugged into the pedestal. Since the fault was downstream of the power protection, it was undetected. They now have a hard-wired PI system that monitors the power just as it goes into the 5th wheel's breaker box.
In your case, the horse is already out of the barn, but HERE is a 1-page explanation of RV 50 amp service.
Rusty
Nice page, you got one for the 30amp circuits that would be a good sticky on anyone's page.
Those basic I & II electronic/electricity courses at the local community college while trying to get an industrial manager degree have sure paid off for me through the years.
To the original poster sorry for your problems a TV and microwave are easy to replace, glad nothing else was messed up bad.
thanks,
randy
โJul-29-2015 07:22 AM
RustyJC wrote:
The repair bill for our daughter and son-in-law's 5th wheel was $7500+ due to a dropped neutral in the RV's power cord that applied 240VAC to all of the 120VAC loads. They had power protection, but it plugged into the pedestal. Since the fault was downstream of the power protection, it was undetected. They now have a hard-wired PI system that monitors the power just as it goes into the 5th wheel's breaker box.
In your case, the horse is already out of the barn, but HERE is a 1-page explanation of RV 50 amp service.
Rusty