A/C off of 20 amp service?

Michigander
Explorer
Explorer
Has anyone ever heard of a single a/c unit not being able to start and run on a 20amp shore power circuit? We bought a new coach and the dealer says don't run a/c unless connected to a 30 amp service or connected to the gen. They say it will cook the compressor. We have always run a/c units in trailers or coaches off a 20 amp circuit without a problem when at home so I am perplexed about what I am missing?? Thoughts?
2008 Winnebago Sightseer 35J
Honda civic toad "RGOCART"

"A father measures his wealth not in his possessions, but in the happiness of his family"
44 REPLIES 44

Effy
Explorer II
Explorer II
Yes, I do it all the time. Worst case it will trip a breaker.
2013 ACE 29.2

time2roll
Nomad
Nomad
pianotuna wrote:
#12 voltage with a 311 watt load was 119.1
#10 voltage with the identical load was 121.
Need second test with real 1500 watt load.

DrewE
Explorer II
Explorer II
pianotuna wrote:
Hi,

I recently compared a #12 100 foot extension cord to a #10 100 foot extension cord on the same 15 amp shore power outlet. The same dog bone adapter was used with both--but obviously in two different places.

#12 voltage with a 311 watt load was 119.1
#10 voltage with the identical load was 121.

So monitor voltage carefully--and consider getting an autoformer.


Based on these tablesl, the difference in resistance between 12 gauge wire and 10 gauge wire is 0.589 ohms per 1000 feet. In your test, you have 200 feet of wire to account for (100 feet coming and 100 feet going), and a test current of about 3 amps, so the voltage difference attributable to the change in wire should be about 0.3 volts. Obviously something else is different--maybe the plugs made better or worse connections, or maybe the voltage at the outlet varied a little between the trials, or maybe the 12 gauge cord has a poor connection at one of its ends.

pianotuna
Nomad III
Nomad III
Hi,

I recently compared a #12 100 foot extension cord to a #10 100 foot extension cord on the same 15 amp shore power outlet. The same dog bone adapter was used with both--but obviously in two different places.

#12 voltage with a 311 watt load was 119.1
#10 voltage with the identical load was 121.

So monitor voltage carefully--and consider getting an autoformer.
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

427435
Explorer
Explorer
I routinely run my Winny basement air conditioning on a 20 amp circuit and an extension cord. I suspect your Winny has a load control panel similar to mine. Just be sure to set it for 20 amps before turning the AC on. Otherwise, the 2nd AC unit will try to start and blow your house breaker.
Mark

2000 Itasca Suncruiser 35U on a Ford chassis, 80,000 miles
2003 Ford Explorer toad with Ready Brake supplemental brakes,
Ready Brute tow bar, and Demco base plate.

CA_Traveler
Explorer III
Explorer III
DownTheAvenue wrote:
CA Traveler wrote:
20A is definitely borderline because of the smaller wiring.

I'd be cautious about running a 15K BTU A/C on 20A.


This post makes no sense. The A/C circuit inside the RV will be a 20 amp circuit wired with a 12 gauge wire and a 20 amp circuit breaker.

What's the difference?
OK but the OP referred to 20A shore plug which will also have the smaller wiring with the additional voltage loss vs a 30A or 50A plug. Plus the OP referred to a 20A home plug.

It's very typical that the problem is not the rig wiring but the voltage drop at the pedestal due to the 20A plug/wiring.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

full-timer
Explorer
Explorer
I found out that running a single a/c unit and making sure the water heaters electric is turned off you will have no problem. Its when the water heater comes on that it will kick the breaker.
An Indian and a Gypsy

Joe and Nancy
2002 34 foot Georgetown double slide Ford V-10
towing 2004 Chevrolet Cavalier 4 Down

time2roll
Nomad
Nomad
DownTheAvenue wrote:
CA Traveler wrote:
20A is definitely borderline because of the smaller wiring.

I'd be cautious about running a 15K BTU A/C on 20A.


This post makes no sense. The A/C circuit inside the RV will be a 20 amp circuit wired with a 12 gauge wire and a 20 amp circuit breaker.

What's the difference?
Depends on the length of the wire in the circuit. Could be 150+ feet depending on conditions. This is why I recommend to check voltage in the RV once running.

time2roll
Nomad
Nomad
Keep the fridge and water on propane only, battery needs to be full charge.
Then let it rip. Do watch voltage is 108+ once the compressor is running smooth.

20 amp could be a generic name for 15 amp or 20 amp circuit so do verify what you have available. Also common to be a shared circuit so other items need to be off.

Michigander
Explorer
Explorer
Old coach was Sightseer 35J, New coach is 2016 Sunstar 31BE.
2008 Winnebago Sightseer 35J
Honda civic toad "RGOCART"

"A father measures his wealth not in his possessions, but in the happiness of his family"

DownTheAvenue
Explorer
Explorer
CA Traveler wrote:
20A is definitely borderline because of the smaller wiring.

I'd be cautious about running a 15K BTU A/C on 20A.


This post makes no sense. The A/C circuit inside the RV will be a 20 amp circuit wired with a 12 gauge wire and a 20 amp circuit breaker.

What's the difference?

Tom_Barb
Explorer
Explorer
Ours simply kicks the Breaker off.
2000 Newmar mountain aire 4081 DP, ISC/350 Allison 6 speed, Wrangler JL toad.

CA_Traveler
Explorer III
Explorer III
20A is definitely borderline because of the smaller wiring. But everything depends upon your A/C draw, other rig draws and the actual voltage.

I'd be cautious about running a 15K BTU A/C on 20A.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

Up_DownDeCoast
Explorer
Explorer
This is going to depend on the size of the A/C unit. If your talking about the rig in your signature (which i also have)you should have no problem. I run one A/C unit when getting ready for a trip or doing maintenance at home. I actually plug into a 15 amp circuit. One of my units pulls about 12 amps. I make sure nothing else is running on that circuit when the A/C is on.
David and Wendy
2008 Winnebago Sightseer 35J
2021 Honda CR-V
Demco KarKaddy SS Tow Dolly

AllegroD
Nomad
Nomad
Sounds like a fair warning, though not fully explained. Depending on the draw and if other things are on a 20amp gang, you might be warned to monitor your power. Get a Kill-A-Watt or volt meter to monitor your 120 voltage. Read your AC manual. Less than 105volts on most AC will cause cumulative heat damage to your AC. This does not show right away but will take years of your AC life. I do not like going below 108 volts.