MrWizard wrote:
he already has a 6500 LP generator
Sep-02-2017 02:34 PM
Sep-02-2017 10:26 AM
Sep-02-2017 09:56 AM
Sep-02-2017 09:21 AM
Sep-01-2017 09:13 PM
Sep-01-2017 06:25 AM
CA Traveler wrote:I don't find anything from Onan that supports your theory Bob, but Onan isn't real open about publishing the install manuals. What I do know, is the Engineers that designed my coach didn't see it necessary to do anything special for the 8000 QD, so I'm sure the OP will be fine not upgrading the wiring or transfer switch. I have the same 50amp rated lugs on my transfer switch that he does on his, and the wiring gauge, including the neutral, coming from the shoreline is the same going to the CB. I don't see where the generator wire size is any larger than the others either. My personal opinion is you are trying to prove a point that has no difference on the outcome.
Mike,
It's not theory - it's basic AC Circuits 101. Have you researched this to where you now understand the QD 8000 has a maximum 66A on the neutral and the RV 50A circuit has a maximum of 50A on the neutral?
Aug-31-2017 07:00 PM
Aug-31-2017 06:14 PM
CA Traveler wrote:
Mike, You've just demonstrated that you don't understand a 120/240V circuit like the 50A RV. That's OK because we all have to learn.
Just so you know both hot's and the neutral are the exact same wire size. The secondary winding on the utility transformer is a single phase center tapped winding and the center tap is the neutral. Due to this type of circuit the center tap or neutral wire carries the difference in amps of the two hots. ie If one hot has 30A and the other 20A then the neutral has 10A. A 120/240V 50A RV circuit neutral does not carry the sum of the two hot lines. Hence none of the 3 wires will carry more than 50A due to the 50A CB on the hot lines.
The QD 8000 has 2 33A 120V circuits and it's common neutral does carry the sum of both of the hot wires. Hence the wiring needs to handle 66A all the way to the CB panel.
Aug-31-2017 05:44 PM
CA Traveler wrote:So you are saying the neutral wire size for an 8000K generator needs to be larger than that for the 50A 240 pedestal shore line to the CB. I think you are totally over thinking this.
Mike, You've just demonstrated that you don't understand a 120/240V circuit like the 50A RV. That's OK because we all have to learn.
Just so you know both hot's and the neutral are the exact same wire size. The secondary winding on the utility transformer is a single phase center tapped winding and the center tap is the neutral. Due to this type of circuit the center tap or neutral wire carries the difference in amps of the two hots. ie If one hot has 30A and the other 20A then the neutral has 10A. A 120/240V 50A RV circuit neutral does not carry the sum of the two hot lines. Hence none of the 3 wires will carry more than 50A due to the 50A CB on the hot lines.
The QD 8000 has 2 33A 120V circuits and it's common neutral does carry the sum of both of the hot wires. Hence the wiring needs to handle 66A all the way to the CB panel.
Aug-31-2017 04:25 PM