Bobbo wrote:Yeah, that is becoming painfully obvious to me as I read these explanations. Too bad they don't tell you that on the box. I could have saved some money.
If you plug into a GFCI outlet with that, it will trip EVERY time. Buying it was a waste of money.
โAug-17-2016 08:05 AM
RoyB wrote:
IVYLOG - guess you are correct with no LIVE male plugs. Each of those two plugs go to either side of the 50AMP zones and not tied together...
Schematic would look something like this one from DMBRUSS
DMBRUSS image
The 30A and 20A Male plug to 50A Female socket adapter is probably wired the same way.
I think it is illegal for companies to sell the adapters that could have live open male plugs...
Roy Ken
โAug-17-2016 07:20 AM
โAug-17-2016 06:40 AM
โAug-17-2016 06:32 AM
โAug-17-2016 05:49 AM
โAug-17-2016 02:52 AM
โAug-16-2016 08:20 PM
โAug-16-2016 08:04 PM
DrewE wrote:Thanks Drew, I had no idea. Sounds like good advice.
I would suggest throwing the "45A" adapter in the trash. IMHO those things are dangerous, or potentially dangerous, especially if there is a fault in the pedestal wiring.
Basically, it connects one leg of the 50A to the 30A plug and the other to the 15A plug. The neutral (and ground) are connected to both. There are several problems or potential problems with this arrangement:
1. As you've found out, it creates (what looks like) a ground fault that will trip a GFCI every time. Since the NEC requires that all 15A or 20A outlets that are outdoors be GFCI protected, the chance of this not happening is quite slim.
2. If there are any 240V devices in your RV (which is not the usual case), you can readily have a live exposed male plug.
3. If there is an outlet with reversed polarity, connecting the adapter creates a short circuit and leaving one end unconnected creates a live male plug.
4. If there is an open or poor neutral connection on one of the outlets, the other neutral may well be overloaded. If the two outlets are on the same phase, it almost certainly will be; and if it's the 30A neutral that's open, the 15A one will carry up to 45A--a quite significant overload, and enough to be more than a theoretical fire hazard.
โAug-16-2016 07:59 PM
โAug-16-2016 07:48 PM
โAug-16-2016 07:33 PM
ChooChooMan74 wrote:Thanks, that is probably the answer. I never checked to see if it's a GFCI circuit but that would make sense.
Those adapters work only in certain instances. For one, the pedestal 15/20 amp can not be a GFI. 2nd, This will only give you about 5400 watts of power instead of the 12000 watts of power that a 50 amp 120/240 connection will give you. So, you are still very limited to what you can use.
โAug-16-2016 07:30 PM
smkettner wrote:Yes, of course. That's exactly what I do every time the 45 amp adapter doesn't work. I just use the regular 30 amp to 50 amp adapter. I was hoping to get 15 more amps so I could use the microwave at the same time as one air conditioner.
Will not work in a GFCI outlet. Will trip every time as designed.
Open leg is because one side is not connected. A regular 30-50 adapter will connect the 30 amps to both your main breakers.
If you can find two outlets without GFCI then it will work. No need to test with a voltmeter. I still do not recommend it. Too much hassle. Your EMS should be able to manage power on 30 amps.... or rather what issue are you trying to resolve?