I recently bought a 2018 Rockwood 5th wheel with a 50 amp service. I have a 240 v 50 amp outlet in my RV cover that Iโ€™ve used for years to plug my motorhome into. Since I still have my motorhome and itโ€™s parked in the RV garage I decided to hook up my 5er temporarily to my 30 amp 240 volt welder outlet. I had no idea that RV 30 amp cords were 120v only. Long story short, after connecting my 30 to 50 adapter I sent 240 volts down one leg of the buss bar. So everything on that side of the bus bar received 240 volts while the other side received zero. My question now is what will I need to replace? My refrigerator, GFCI, rooftop A/C were all on that side. The A/C seems to be working fine, but the fridge isnโ€™t and the GFCI is smoked. Although Iโ€™ve wired up many homes, I certainly learned something about RVโ€™a and their wiring today. Iโ€™m hoping just the circuit board on the fridge can be replaced. Anyone else have any experience with this? Iโ€™m sure this canโ€™t be the first time this has happened. Stupid me!!

2021 Grand Design Reflection 337 RLS
2019 GMC Duramax 4x4

40 REPLIES 40

westernrvparkow
Explorer
Explorer
cavie wrote:
mxdad777 wrote:
BB_TX wrote:
If you used a standard 50/30 dogbone adapter be aware that the adapter connects both hot legs of the coach together. Meaning you put 240 on both hot legs, not just one.

Thatโ€™s what I used, however when I tested both buss bars only one had 240v. The other bar was dead.


You did not have 240 on 1 buss bar, you had 120 on the buss bar and 120 on the neutral. 240 between hot and neutral.
You are new to these forums. You will soon discover that with all the misinformation about electrical service it is a wonder that natural selection hasn't cleaned out the well meaning, but erroneous posters. You are absolutely correct in your diagnosis, but it will be lost in a sea of erroneous posts.

BB_TX
Nomad
Nomad
cavie wrote:
BB_TX wrote:
If you used a standard 50/30 dogbone adapter be aware that the adapter connects both hot legs of the coach together. Meaning you put 240 on both hot legs, not just one.


You can not put 240 volts down both legs. A 30/50 adaptor takes the one 30 amp 120 volt leg and puts that 120 volt leg on the 2 120 volts legs of the 50 amp cord. 120 volts @ 30 amps down both legs.

A 50/30 adaptor takes just 1 50 amp leg and put in down the 1 hotleg of a 30 amp cord.

you can not get 240 volts on one leg of a service in the US and Canada. That only happens in european countries.

An adapter to connect a 50 amp RV to a standard 30 amp outlet connects the 30 amp hot leg to BOTH of the 50 amp RV hot legs. The two hot legs are connected internally in the adapter. Otherwise if you connected a 50 amp RV to a park 30 amp outlet you would only have 120 vac to half the RV. And that just ainโ€™t how it works. And that type adapter is what he said he used. I said 50/30. Thank you for the correction to 30/50.

cavie
Explorer
Explorer
mxdad777 wrote:
I changed the welder receptacle to one that would fit my RV. My mistake was thinking both the 30amp and 50amp RV outlets were both 240v. I knew everything in the RV ran off of 120v, but figured it was the same configuration for both 30 and 50. When I tested the buss bars in the panel, I indeed had 240v on one leg and zero volts on the other. I checked the glass fuse on the fridge circuit board and unfortunately the fuse is good. My guess is the circuit board is toast. Since the microwave and AC unit seem to be working fine, Iโ€™m hopeful the only damage was to the fridge. I think my converter should be fine, because itโ€™s fed off the buss bar that had zero power going to it.


Your gonna fix the welder outlet like it was RIGHT!
2011 Keystone Sprinter 323BHS. Retired Master Electrician. Retired Building Inspector.

All Motor Homes are RV's. All RV's are not Motor Homes.

cavie
Explorer
Explorer
mxdad777 wrote:
I changed the welder receptacle to one that would fit my RV. My mistake was thinking both the 30amp and 50amp RV outlets were both 240v. I knew everything in the RV ran off of 120v, but figured it was the same configuration for both 30 and 50. When I tested the buss bars in the panel, I indeed had 240v on one leg and zero volts on the other. I checked the glass fuse on the fridge circuit board and unfortunately the fuse is good. My guess is the circuit board is toast. Since the microwave and AC unit seem to be working fine, Iโ€™m hopeful the only damage was to the fridge. I think my converter should be fine, because itโ€™s fed off the buss bar that had zero power going to it.


You did not have 240 one leg. You had 120 on one leg and 120 on the neutrals.
2011 Keystone Sprinter 323BHS. Retired Master Electrician. Retired Building Inspector.

All Motor Homes are RV's. All RV's are not Motor Homes.

cavie
Explorer
Explorer
mxdad777 wrote:
BB_TX wrote:
If you used a standard 50/30 dogbone adapter be aware that the adapter connects both hot legs of the coach together. Meaning you put 240 on both hot legs, not just one.

Thatโ€™s what I used, however when I tested both buss bars only one had 240v. The other bar was dead.


You did not have 240 on 1 buss bar, you had 120 on the buss bar and 120 on the neutral. 240 between hot and neutral.
2011 Keystone Sprinter 323BHS. Retired Master Electrician. Retired Building Inspector.

All Motor Homes are RV's. All RV's are not Motor Homes.

DougE
Explorer
Explorer
Scary reading. A lot of ignorance here! A 240v fully wired outlet is 120v, 120v, neutral, ground (4 wires). From there you can drop down to pretty much anything you want with the correct adapters.
Currently Between RVs

cavie
Explorer
Explorer
BB_TX wrote:
If you used a standard 50/30 dogbone adapter be aware that the adapter connects both hot legs of the coach together. Meaning you put 240 on both hot legs, not just one.


You can not put 240 volts down both legs. A 30/50 adaptor takes the one 30 amp 120 volt leg and puts that 120 volt leg on the 2 120 volts legs of the 50 amp cord. 120 volts @ 30 amps down both legs.

A 50/30 adaptor takes just 1 50 amp leg and put in down the 1 hotleg of a 30 amp cord.

you can not get 240 volts on one leg of a service in the US and Canada. That only happens in european countries.
2011 Keystone Sprinter 323BHS. Retired Master Electrician. Retired Building Inspector.

All Motor Homes are RV's. All RV's are not Motor Homes.

mxdad777
Explorer
Explorer
BB_TX wrote:
If you used a standard 50/30 dogbone adapter be aware that the adapter connects both hot legs of the coach together. Meaning you put 240 on both hot legs, not just one.

Thatโ€™s what I used, however when I tested both buss bars only one had 240v. The other bar was dead.

2021 Grand Design Reflection 337 RLS
2019 GMC Duramax 4x4

mxdad777
Explorer
Explorer
I changed the welder receptacle to one that would fit my RV. My mistake was thinking both the 30amp and 50amp RV outlets were both 240v. I knew everything in the RV ran off of 120v, but figured it was the same configuration for both 30 and 50. When I tested the buss bars in the panel, I indeed had 240v on one leg and zero volts on the other. I checked the glass fuse on the fridge circuit board and unfortunately the fuse is good. My guess is the circuit board is toast. Since the microwave and AC unit seem to be working fine, Iโ€™m hopeful the only damage was to the fridge. I think my converter should be fine, because itโ€™s fed off the buss bar that had zero power going to it.

2021 Grand Design Reflection 337 RLS
2019 GMC Duramax 4x4

BB_TX
Nomad
Nomad
If you used a standard 50/30 dogbone adapter be aware that the adapter connects both hot legs of the coach together. Meaning you put 240 on both hot legs, not just one.

cavie
Explorer
Explorer
mxdad777 wrote:
I recently bought a 2018 Rockwood 5th wheel with a 50 amp service. I have a 240 v 50 amp outlet in my RV cover that Iโ€™ve used for years to plug my motorhome into. Since I still have my motorhome and itโ€™s parked in the RV garage I decided to hook up my 5er temporarily to my 30 amp 240 volt welder outlet. I had no idea that RV 30 amp cords were 120v only. Long story short, after connecting my 30 to 50 adapter I sent 240 volts down one leg of the buss bar. So everything on that side of the bus bar received 240 volts while the other side received zero. My question now is what will I need to replace? My refrigerator, GFCI, rooftop A/C were all on that side. The A/C seems to be working fine, but the fridge isnโ€™t and the GFCI is smoked. Although Iโ€™ve wired up many homes, I certainly learned something about RVโ€™a and their wiring today. Iโ€™m hoping just the circuit board on the fridge can be replaced. Anyone else have any experience with this? Iโ€™m sure this canโ€™t be the first time this has happened. Stupid me!!


Happens all the time with DIY electricians and some real electricians when it comes to RV's because they do not read the information printed right on the plugs and receptacles.

1st, you adaptor should not have fit into a 30 amp 240 volt outlet. Seems that you have the wrong outlet and cord for your welder. The problem usually comes when a electrician or DIY wire 240 volts to a 120 volt RV receptacle. Which sounds like what you have done with your welder. I would start by fixing that first. A 120 volt 30 amp RV male plug cannot physically fit into a 30 amp 240 volt female outlet. You didn't run 240 down one leg but you did run 120 down the neutral leg.


Fridge, Furnace, Water Heater all have circuit boards that can be replaced. Fridge will have a glass fuse in back that may have blown and saved the fridge. Microwave also has an internal fuse.
2011 Keystone Sprinter 323BHS. Retired Master Electrician. Retired Building Inspector.

All Motor Homes are RV's. All RV's are not Motor Homes.