myredracer wrote:
In Canada, it is acceptable by code to connect & operate fixed heating appliance loads (baseboards, eg.) at 100 percent of the heating circuit's breaker size. Basically in an RV, you can plug in as much stuff as you want until the 30 amp breaker in the pedestal or converter/panel trips, then you'll know it was too much.
โMar-18-2017 07:09 AM
GordonThree wrote:Sorry, but that is incorrect. I saw someone post this in another thread the other day and warrants correcting.
Yes a 30a circuit is only good for 23-26 amps continuous duty, the microwave counts as an intermittent load.
โMar-17-2017 03:49 PM
tinstartrvlr wrote:
Think a new 20 amp circuit is the best way to go, based on what everyone is posting here.
Seems simple enough to just add another 20 amp circuit; but not sure I could add it to the existing panel. There would be room on the wall to add another small breaker next to the panel if necessary. It is a straight shot from the box to the outside wall, through the kitchen sink cabinet, unlike the current 30 amp inlet. (why the mfg put the inlet 20 wire feet away from the box baffles me!)
I haven't looked online yet to see if there is a 20amp connector that I can put on the outside of the TT, but thinking there must be one somewhere. Or can I just use another 30 amp connector and an adapter at the pedestal?
Thinking this is doable at not a huge cost!
โMar-17-2017 03:21 PM
โMar-17-2017 02:24 PM
โMar-17-2017 01:19 PM
MrWizard wrote:
You don't need a 50 amp service, or even one leg of the 50 amp to run one a/c
Remove the a/c circuit from the breaker in the panel
Get a small double breaker box, but in a 20 amp c.f., Conner the a/c to that
Run a new cord circuit 12 gauge from box to o outside with a 15 or 20 amp duplex make plug on the end
A single 20 circuit from the power pole is all you need for the air
And this will work every where
Not all camp grounds have 50 plugs
Do that or change the th over to 50 amp service with new breaker panel and new 50 amp cord
โMar-17-2017 10:59 AM
โMar-17-2017 08:25 AM
โMar-17-2017 08:22 AM
tinstartrvlr wrote:
Piano,
Regardless of what I do, I think I might add that capacitor anyway. Looks like it would be a good thing to have no matter what.
As long as the 20 amp circuit is enough to handle the startup, that makes the most sense. I could also use that circuit for a space heater in the winter as well.
And with 20 amp, I likely won't run into the issue of no hookup at a campground like sometimes happens when there are no 50 amp hookups.