brulaz wrote:Itinerant1 wrote:
...
I'm using the PT100 and it does integrate nicely with the Magnum inverter/ charger (hybrid) following the settings set throught the Me-Arc. This is with GBS LiFePo4 Batteries which have their own EMS CPU (shunt and more) so no BMK.
...
Off-topic, but I gotta ask:
GBS makes LiFeMnPO4 batteries, but I've never seen them advertise their own BMS (or EMS). Could you provide more detail about your BMS and/or where you got the system?
I suppose the basic idea is the same: like Mex says, you don't want to overcharge an AGM (or undercharge it). And you can use something like Magnum's BMK to be sure you don't. A Li battery's BMS provides the same function and cell balancing as well as other protections, depending upon the BMS.
Heck, for my 24V system I even have a Victron Battery Balancer that ensures the two 12V banks in series are charged properly (they are different brands and ages). A Li BMS should do the same but at the individual cell level.
โApr-29-2018 03:57 PM
Itinerant1 wrote:
...
I'm using the PT100 and it does integrate nicely with the Magnum inverter/ charger (hybrid) following the settings set throught the Me-Arc. This is with GBS LiFePo4 Batteries which have their own EMS CPU (shunt and more) so no BMK.
...
โApr-29-2018 04:40 AM
Itinerant1 wrote:
I'm using the PT100 and it does integrate nicely with the Magnum inverter/ charger (hybrid) following the settings set throught the Me-Arc. This is with GBS LiFePo4 Batteries which have their own EMS CPU (shunt and more) so no BMK.
The PT100 will work with 12v panels except they need to be in series. Mine are 160w (22.50 VOC) panels, 2 in series 4 sets parallel to combiner box, 1,280w. On occasion I will get P04 code which is "Power Limited" (Internal Frequency) happens at +/- 1,150w _ 75-80a area. It's been in service for 2 years now fulltime with no apparent problems.
I spoke with the installer and some systems don't like the PT100 with the lower voltage from panels and he corrected the issue, don't know if that was using a different controller or added panels in series.
โApr-28-2018 06:13 PM
jharrell wrote:
The PT-100 has nice integration to be sure, I would have gone with it except that it won't use panels below 24V on a 12V system. I have 12V (20 VOC) panels in parallel and didn't want to go to series yet, so I went with a Tristar MPPT 60 which has no issue.
Works ok with two independent systems, they basically communicate with voltage, have the solar set slightly higher for charge settings so it tends to be dominant but when batteries are down both go into bulk and both contribute.
The Magnum network is actually not that complicated, just a RS-485 bus with the inverter as master sending it state at 10hz, the remote sends its config right after, then BMK and AGS at 1hz, not sure about PT-100 probably similar to BMK. I have written some software to display the info on a web page using a $5 USB dongle and a Raspberry pi. I also show my Tristar info on the same page as it has ethernet and does modbus.
โApr-28-2018 04:45 PM
brulaz wrote:
WRT the Magnum inverter/charger and BMK+shunt:
Apparently Magnum's MPPT solar charger can be networked in along with the BMK+shunt and ARC (advanced remote control). It can be controlled by the ARC and inverter/charger settings so the BMK's estimate of battery SOC can be used to terminate absorb from solar charging as well as from shorepower charging.
But if instead you use a NON-Magnum, NON-networked solar charger, things might go awry with the Magnum's logic?
Pretty complicated networked system:
โApr-28-2018 04:45 PM
โApr-28-2018 09:50 AM
pianotuna wrote:
Hi brulaz,
No, I am shunt free.
All I can say is I get to 0.5 amps per 100 amp-hours of capacity.
...
โApr-28-2018 09:44 AM
โApr-28-2018 09:09 AM
MrWizard wrote:
To know the amps charger into the battery
Install a separate amp meter for the battery,
Or
Turn off all 12dc loads, lights, water pump etc.. Turn off any stand alone inverter, except the fridge parasitic control
And see what your Magnum displays says
The low milliamp draw of the fridge will be negligbile
The display will reflect the charge amps
โApr-28-2018 09:08 AM
pianotuna wrote:
...
May I ask you to reduce the width of your picture--it makes reading the thread hard when it is so wide. (I use 375)
โApr-28-2018 09:02 AM
โApr-28-2018 08:51 AM
pianotuna wrote:
My Magnum plays well with my Blue Sky 3024di solar controller.
โApr-28-2018 08:16 AM