Air conditioner woes

Veebyes
Explorer II
Explorer II
Recently replaced fan motor & capacitor. Fan works fine. The issue is that the compressor kicks in, runs fine & quiet for awhile then gets very noisy, amperage draw goes way up, then it trips the overload breaker on my inverter charger shutting all power off tothe trailer. What is preventing the compressor from shutting off? Considering connecting the original capacitor again.
Boat: 32' 1996 Albin 32+2, single Cummins 315hp
40+ night per year overnighter

2007 Alpenlite 34RLR
2006 Chevy 3500 LT, CC,LB 6.6L Diesel

Ham Radio: VP9KL, IRLP node 7995
24 REPLIES 24

dougrainer
Nomad
Nomad
S Davis wrote:
wa8yxm wrote:
You have described a clogged condenser coil. or restricted air flow in the area of the condenser coil.


Or low refrigerant charge.


Really? LOW charge or NO charge will cause LOW amp draw. Doug

allen8106
Explorer
Explorer
Deleted.
2010 Eagle Super Lite 315RLDS
2018 GMC Sierra 3500HD 6.6L Duramax

2010 Nights 45
2011 Nights 70
2012 Nights 144
2013 Nights 46
2014 Nights 49
2015 Nights 57
2016 Nights 73
2017 Nights 40
2018 Nights 56
2019 Nights 76
2020 Nights 68

time2roll
Nomad
Nomad
Veebyes wrote:
A Magnum 2000w pure sine wave unit. The draw on the leg that the AC is on goes up to 27 amps before breaker on the Magnum trips. So is a new AC unit in my future?
Yes time for a new complete high efficiency A/C unit.

This is why I would never pay to repair one of these things. Once it starts to fail the big stuff is ready to go and you are still stuck with an old inefficient power hog.

27 amps will be indicating the compressor is shot.

S_Davis
Explorer
Explorer
wa8yxm wrote:
You have described a clogged condenser coil. or restricted air flow in the area of the condenser coil.


Or low refrigerant charge.

pianotuna
Nomad III
Nomad III
Ah but with hybrid inverters that do load support it IS desirable to pass power through the inverter.

Veebees, I think your air conditioner is 3/4 way to AC heaven. I would try the old cap. If that doesn't make a difference then it may be toast.

How is the voltage just before the unit trips the breaker?
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

dougrainer
Nomad
Nomad
Veebyes wrote:
This does not look good. In the process of fan motor replacement I did take the opportunity to clean everything. Took the inner shroud off & cleaned the fins, clogged, using a soft brush & compressed air. Thoroughly cleaned fans while at it. Re the inverter charger. It has been installed for 8 years. Not your typical cheap RV unit. A Magnum 2000w pure sine wave unit. The draw on the leg that the AC is on goes up to 27 amps before breaker on the Magnum trips. So is a new AC unit in my future?

Yes, more cost effective to replace unit. Your Inverter is used on MANY Motorhome units, in fact, LARGER Inverter/chargers. It is still not a good idea to run the AC circuit thru the Inverter system. While you do it and a lot do that, it is not the best way to run the electrical. Doug

wolfe10
Explorer
Explorer
This should NOT be run through your inverter.

Per your post, 27 amps times 120VAC= 3,240 watts. Even assuming 100% inverter efficiency, this is WAY overloading a 2000 watt inverter. Even on shore power, very much doubt the pass through relay is happy with that start up load.
Brett Wolfe
Ex: 2003 Alpine 38'FDDS
Ex: 1997 Safari 35'
Ex: 1993 Foretravel U240

Diesel RV Club:http://www.dieselrvclub.org/

Veebyes
Explorer II
Explorer II
This does not look good. In the process of fan motor replacement I did take the opportunity to clean everything. Took the inner shroud off & cleaned the fins, clogged, using a soft brush & compressed air. Thoroughly cleaned fans while at it. Re the inverter charger. It has been installed for 8 years. Not your typical cheap RV unit. A Magnum 2000w pure sine wave unit. The draw on the leg that the AC is on goes up to 27 amps before breaker on the Magnum trips. So is a new AC unit in my future?
Boat: 32' 1996 Albin 32+2, single Cummins 315hp
40+ night per year overnighter

2007 Alpenlite 34RLR
2006 Chevy 3500 LT, CC,LB 6.6L Diesel

Ham Radio: VP9KL, IRLP node 7995

wa8yxm
Explorer III
Explorer III
You have described a clogged condenser coil. or restricted air flow in the area of the condenser coil.

What is happening:
As the A/C "Pumps" heat from inside (Evaporator) to outside (Condenser) if the condenser can not shed the heat fast enough the heat builds inside the system and pressure goes up. The compressor works harder and harder. The type of motor they use in the compressor the harder it works the more current it draws And finally CLICK.

Clean the condenser

Now on most (All but colemen) you remove the outer shroud
Then you have to remove an inner cover.

YOu can then access the "Back side" (Fan side) of the condenser. Take a look you will likely see it clogged.. If your hands are small enough you may be able to reach in and clean or use a long thin brush to clean gently (Be very gentle you do not want to mess up the fins).. Compressed air is also useful.

On Coleman. You only need remove the outer cover since the fan sucks instead of blowing.
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times

dougrainer
Nomad
Nomad
1. You are not supposed to connect a hi amp appliance like a AC unit to the Inverter/Charger.
2. I assume you are running ALL 120 loads thru the Inverter/Charger. Is this so?
3. Compressor's that run normal then slowly increase the amp draw until the Breaker trips usually means a BAD compressor. Doug