Atwood 7900 series furnace troubleshooting

obscenic
Explorer
Explorer
I have a brand new 7916-II installed in my small coach. Thermostat is brand new, t-stat wiring is brand new.

The furnace gets most of the way through the ignition cycle before failing.

1. T-stat closes correctly
2. Fan motor spins up
3. Sail switch closes
4. Gas valve opens
5. Igniter sparks for 6-7 seconds
6. No ignition
7. Igniter waits, then sparks again.
8. No ignition
9. Igniter waits, then sparks again.
10. No ignition
11. Blower stops. Red LED blinks 3 times indicating Ignition Lockout Fault.

About ONE in ten times it works. No rhyme or reason. Sometimes it fires up first try.

Options ruled out:
-All components are new
-Vent/intake are not blocked in any way
-Power supply is a steady 12.2vdc
-Propane supply hasn't been tested yet, but not sure that it would ever work if the pressure were too low. Propane tank is newly filled.
8 REPLIES 8

obscenic
Explorer
Explorer
I forgot to post my results from when I actually traced the issue. It was resolved on page 4 of this thread:

http://www.rv.net/forum/index.cfm/fuseaction/thread/tid/27915352/srt/pa/pging/1/page/3.cfm

obscenic
Explorer
Explorer
So I have 11 WC" at the regulator, so that's not the problem. I'm measuring 6 at the valve outlet, but perhaps that is correct, since half of the pressure would be going into the burner head?

obscenic
Explorer
Explorer
With so many brilliant minds here pointing towards the propane flow, I built a manometer, and to my dismay, I'm only getting about 6" W.C. at the valve! Guess I need to track that down before I try anything else.

jetcare
Explorer
Explorer
Loosen the propane line going to the furnace just a bit and see if you get propane flow. If you do, retighten propane line and wait 10 minutes. Stand outside by the furnace and have someone operate the thermostat. Stick you nose up near the exhaust pipe but keep your face away from the pipe. (Do you smell propane during and right after each ignition attempt). If you do, you have an igniter placement problem or an igniter lead wire that is shorted somewhere allowing the spark to jump to ground and not through the igniter.

If you don't smell propane,(which is usually what I find) remove the burner assembly and inspect the LP orifice. I normally find a bug inside the orifice.

All this is assuming you described your problem correctly and you have no LP ignition, not even 2-5 seconds worth.
2016 F-250 Crewcab 6.2L 4x4
2012 Palomino Sabre 32' Travel Trailer

Old-Biscuit
Explorer III
Explorer III
Spark electrode not properly positioned....

Needs to be directly over the burner slots and the gap needs to be 1/8" (tip to rod).

Also burner slots need to be clear of any rust/debris etc. that would disrupt gas flow.
Is it time for your medication or mine?


2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
US NAVY------USS Decatur DDG31

ScottG
Nomad
Nomad
Sounds like it's not getting enough gas. Crack the line going to it to bleed air out. Does the stove get a nice strong flame?

obscenic
Explorer
Explorer
Regulator is nearly brand new too...

newman_fulltime
Explorer II
Explorer II
change your regulator out its bad and not giving enough pressure