We have a Brand new park model with an Atwood gas furnace
Tonight before we left the campground I tried to turn on the furnace and the fan(blower) would turn on and off over and over, but would not ignite. I did not hear the usual clicking as I did before. The fan after turning on and off a few times would trip the GFI circuit. I reset the circuit and tried again but same thing happened.
When I look at the circuit board in the furnace, it has a red light that stays on.
What could be the problem
Thank you
Barry
5 REPLIES 5

Old-Biscuit
Explorer III
Explorer III
BFL13 wrote:
OP says it is in a park model. Park model furnaces have gas with AC and DC voltages.

https://pantherrvproducts.com/dometic-atwood-31095-afl-furnace-ac-to-dc-transformer/


That is why MODEL Number is needed.
Atwood AC Models use 24VDC as control circuit to trigger the 120VAC circuits

Would imagine it is a 8900 Series
Issue could be with the AC/DC Transformer OR the Timed Delay Relay
Is it time for your medication or mine?


2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
US NAVY------USS Decatur DDG31

BFL13
Explorer II
Explorer II
OP says it is in a park model. Park model furnaces have gas with AC and DC voltages.

https://pantherrvproducts.com/dometic-atwood-31095-afl-furnace-ac-to-dc-transformer/
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

Old-Biscuit
Explorer III
Explorer III
Model of Furnace???

Fan on/off over and over suggests issue with 'Blower' circuit on furnace circuit board
OR issue with thermostat

DC Voltage is at furnace waiting for dc signal from thermostat ....when received the FAN starts/purges and makes up sail switch to allow DC to 'Power circuit'

Model of furnace??
Is it time for your medication or mine?


2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
US NAVY------USS Decatur DDG31

jdc1
Explorer II
Explorer II
Is the propane on? Did you purge the lines?

Ed_Gee
Explorer II
Explorer II
You should seek and download the user manual for whatever furnace model you have. They all contain very helpful troubleshooting procedures. Is this an RV or a house you have? I am curious what your GFI has to do with the furnace. Every RV furnace I have seen runs totally on 12VDC and has nothing to do with 120VAC......