dougrainer wrote:
The BLUE wires just send a 12 volt signal to the furnace to ACTIVATE the furnace to heat. Once the Blue wire sends the 12 volt signal the Fan relay is energized and the motor should come ON. NOTHING will happen until the Fam motor runs. So, you need to jump the 2 blue wires AT the furnace, not at the Tstat. Also, ONE of those blue wires must have 12 volts positive. So, IF you have no 12 volts at either BLUE wires that is the start of your problem. The blue wires start at your furnace and the Furnace supplies one of those Blue wires with the required 12 volts. It makes no difference which blue wire has the 12 volt power, just one of them. Doug
โApr-29-2019 05:03 AM
โApr-29-2019 04:56 AM
โApr-28-2019 10:47 PM
โApr-11-2018 11:28 AM
โApr-10-2018 04:20 PM
Sodakdave wrote:
Was this ever resolved? I have the exact same issue.
โApr-10-2018 04:08 PM
โOct-20-2013 02:35 PM
Golden_HVAC wrote:
My guess is that the furnace stopped working, and then you tried changing the cylinders, and then found it is still not working...
โOct-20-2013 12:29 PM
โJan-08-2013 04:30 PM
โJan-07-2013 07:04 AM
โJan-07-2013 04:16 AM
snowdance wrote:
X-2 what eHoefler said. Turn propane off and on again very slow.