cancel
Showing results forย 
Search instead forย 
Did you mean:ย 

Coverter/ GFCI problems

Usnthedog
Explorer
Explorer
Brand new Grand Design Reflection 5er (50A). Just home from the lot. Plugged into my shore power (20A) and tripped the GFCI. Changed cord and different GFCI. Still tripped it. Moved to a non GFCI circuit and ran the Refrig to get ready for a weekend trip. Everything worked. Home from the weekend with no problems and started chasing problem. Checked resistance between ground and hots at the RV and 'open'. Used original set up; 50' 12ga cord, 20a-30a and a 30a to 50a adapter, no load. OK. Plugged into rv and tripped the GFCI. Threw the converter breaker and no trip. Dual fuel refrig ran. On demand water heater so nothing there. Ran 30 minutes or more. Turned on the converter breaker and in less than 3 minutes tripped the GFCI. Sounds like a bad converter. Does anyone have a different idea? I have no information on the converter (don't even kn0w where it is).

Thanks,
Jeff.
21 REPLIES 21

BFL13
Explorer II
Explorer II
So at the campground no problems. Not a GFCI at pedestal. So it happens at home with a GFCI plug-in at stick house. Assuming the GFCIs that trip in the OP are stick-house?

Usually it is an adapter in the shore power cable string of cables from the RV.

Or the converter could be sharing its 120v CB with some 120 receptacles where one might have something plugged in that is tripping the house GFCI. Not the converter. You don't know if it is the converter (under warranty)
The outside 120v plug in can get wet while washing the RV too.

IMO live with it by using only non-GFCI plug-ins until it is convenient to get them to do the warranty work. Not to lose any camping time waiting for them
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
2. 1991 Bighorn 9.5ft Truck Camper on 2003 Chev 2500HD 6.0 Gas
See Profile for Electronic set-ups for 1. and 2.

Usnthedog
Explorer
Explorer
wa8yxm and 3 tons. Thanks. Please reread my OP. No hot water heater. (on demand propane only) Only with the converter breaker on doe it trip. Checked continuity between ground and hot on the outside entrance plug. No onboard generator. Refer on caused no problem. Only when the converter breaker is on. And please don't get upset with "please reread the post" it wasn't intended like you thought it was.

Thanks

Jeff

road-runner
Explorer III
Explorer III
It could be a case of the manufacturer driving a staple through a power wire. Wouldn't be the first time.
2009 Fleetwood Icon

CA_Traveler
Explorer III
Explorer III
With the converter model search for your problem for both the RV and converter.

Although less likely the problem could be the wiring from the CB to the converter.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

CA_Traveler
Explorer III
Explorer III
Find the converter. If it's a charger/inverter with AC output for pass though then the AC output(s) wiring/appliances wcould be causing the problem.

Try another location with a GFCI and if it fails then have it fixed under warranty. Any change you make could void the warranty.

FYI Dealers are usually busy during the summer months and if they give you a long date insist that this is a safety issue and you want it fixed very quick.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

3_tons
Explorer III
Explorer III
Using a continuity meter, I would first confirm (with camper unplugged from shore) that there exist NO continuity between neutrals and grounds at campers main panel, meaning, no undesirable โ€˜eddy currentsโ€™ causing the shore GFI trippingโ€ฆ

Note however, that IF you have an onboard genny or inverter, bonding of neutral to ground may be happening passively at either device via a โ€˜floating groundโ€™โ€ฆ

Outside of that, it could be a defective leakage within the hot water heater or refer (an electrode element, neutral to ground affairโ€ฆ), or (since it is a new rig) more likely, it could simply be that this fussy home GFI is โ€˜daisy chainedโ€™ (to save builder moola) into far too many receptacles - try dedicating this home GFI circuit to strictly just the camper by temporarily UNPLUGGING all relevant home appliances on that particular GFI circuit, then try again..

3 tons

wa8yxm
Explorer III
Explorer III
Well not all RV's play nice with GFCI outlets..
Some the converter seems to be the issue if the batteries are "Hungry"
Some if the batteries are "Full"
Some it seems not to matter
Some it's not the converter.
There is a whole list of "Suspects"
Start by turning off all breakers in RV
Plug the RV into a GFCI outlet and plug a drop cord (Trouble lamp) into the other half of that GFCI protected outlet

Now put the lamp where you can see it inside the RV
Turn on the main, Lamp still on good
Turn a branch circuit, and another and another till the light goes out.
NOTE THAt one . turn off, reset GFCI and continue till all breakers are either ON or NOTED.. now you have a suspect list (What that breaker powers)
Home was where I park it. but alas the.
2005 Damon Intruder 377 Alas declared a total loss
after a semi "nicked" it. Still have the radios
Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times