May-09-2021 02:23 PM
May-19-2021 03:05 PM
May-17-2021 04:12 PM
NKnowland wrote:
Yes! Obstructed burner was the culprit. Thanks so much.
May-17-2021 02:03 PM
NKnowland wrote:NRALIFR wrote:
I’d get a second opinion on that burner, or buy a manometer and check the LP pressure myself. It should be at least 11” wc WITH the LP system loaded about 50%, which means you ought to be running the furnace and water heater while checking the pressure.
I just noticed you said new baffle, so I removed that suggestion.
Seriously, check the LP pressure again. The flame can LOOK good, but still be too low btu-wise.
:):)
We’ve got a manometer and it reads 11.2 under load,
May-17-2021 01:58 PM
May-17-2021 01:57 PM
Old-Biscuit wrote:
Freezer/Food compartment get cold on AC element and stays cold on DC element
But freezer only gets cold (not the food compartment) when using GAS
That means GAS is NOT generating ENOUGH hot ammonia vapor.....
Low LP System Pressure causes cool gas flame cause insufficient boiling of ammonia into hot vapor
*freezer is first in coolant flow......freezer gets cold cause there is enough absorption but not enough for food compartment
LP System Pressure OR obstructed burner orifice inhibiting the gas flow to burner
YES! Cleaned the burner yet again. And that was it. The end of a long, frustrating journey!
Side note:
'Fridge'----that is the whole unit Freezer AND food compartment
'Fridge' is short for Refrigerator
May-10-2021 05:16 AM
May-10-2021 04:51 AM
May-09-2021 09:49 PM
NRALIFR wrote:
I’d get a second opinion on that burner, or buy a manometer and check the LP pressure myself. It should be at least 11” wc WITH the LP system loaded about 50%, which means you ought to be running the furnace and water heater while checking the pressure.
I just noticed you said new baffle, so I removed that suggestion.
Seriously, check the LP pressure again. The flame can LOOK good, but still be too low btu-wise.
:):)
May-09-2021 09:46 PM
John Wayne wrote:
Make sure the flame is going up the center of the tube.
May-09-2021 09:45 PM
NRALIFR wrote:Old-Biscuit wrote:
………
LP System Pressure OR obstructed burner orifice inhibiting the gas flow to burner
……….
That’s a good point, an obstructed orifice could result in the same symptoms as low LP pressure. Soak it in alcohol then blow it out to clean it, or just replace it.
It’s clearly an issue of not enough heat BTU’s are going into the cooling unit when running on LP, so the cooling unit performance is degraded. On mine, the flame produced with low LP pressure looks virtually the same as the flame produced with correct pressure. The only thing that’s noticeably different to me is the SOUND the flame makes. When the pressure is low, it’s almost silent. When the pressure is correct I can hear the flame without even removing the outside panel. I didn’t even realize that until I bought a manometer and adjusted the LP pressure myself. After adjusting it and hearing the flame, it was an “Oh yeah, I remember that sound now” moment for me.
And yes, get a wireless fridge thermometer that will let you monitor the fridge and freezer temps without opening the doors. My fridge, which is probably smaller than the average fridge because it’s in a truck camper, will cool down quite rapidly on AC or LP when it’s working right. When something is wrong, I can tell pretty quickly.
We have a manameter and got a reading of 11.1 under loaf.
How did you adjust the LP pressure yourself? It doesn’t seem obvious which direction to turn.
:):)
May-09-2021 09:39 PM
BFL13 wrote:yes to both
It is not the thermistor because it works ok on 120v?
Does the light come on when you open the door? ISTR that is related to the thermistor getting 12v. Vague on that!
May-09-2021 09:37 PM
ksg5000 wrote:Trust me, I’ve given it days to cool. And yes, we have a remote thermometer to monitor .
Fridge sounds like it works fine - you just need to develop patience. Let it cool overnight and then check. Quit opening the door and checking - buy a remote thermometer if you feel you have to monitor. Common problem for new RVers.
May-09-2021 09:25 PM
May-09-2021 06:02 PM
Old-Biscuit wrote:
………
LP System Pressure OR obstructed burner orifice inhibiting the gas flow to burner
……….