โSep-10-2019 12:18 PM
โSep-11-2019 04:15 PM
DFord wrote:sayoung wrote:
FYI, the RUN capacitor only works at STARTUP. At roughly 70% of full rpm " back electromotive force , EMF " stops current flow thru start winding. .
Yes it's got symptoms of a a bad run cap but again what's the amp draw & voltage ?. Could be a bad wire terminal, locked compressor, on and on.
https://yorkcentraltechtalk.wordpress.com/2012/03/30/everything-you-ever-wanted-to-know-about-capaci...York Central Tech Talk wrote:
The RUN capacitor is wired in series with the start winding of the motor and stays in the circuit all of the time. They are designed to dissipate heat associated with continuous operation of the motor. The whole purpose of the RUN capacitor is to bring the start winding back in phase with the run winding. The start winding is slightly out of phase with the run winding to provide starting torque for the motor. The RUN capacitor also provides โrunning torqueโ once the motor is up and running.
As you can see from the information above, the RUN capacitor is ALWAYS IN THE CIRCUIT helping the compressor / fan / any PERMANENT SPLIT CAPACITOR (PSC) motor perform better. sayoung before you start correcting people, educate yourself.
โSep-11-2019 08:29 AM
sayoung wrote:
FYI, the RUN capacitor only works at STARTUP. At roughly 70% of full rpm " back electromotive force , EMF " stops current flow thru start winding. .
Yes it's got symptoms of a a bad run cap but again what's the amp draw & voltage ?. Could be a bad wire terminal, locked compressor, on and on.
York Central Tech Talk wrote:
The RUN capacitor is wired in series with the start winding of the motor and stays in the circuit all of the time. They are designed to dissipate heat associated with continuous operation of the motor. The whole purpose of the RUN capacitor is to bring the start winding back in phase with the run winding. The start winding is slightly out of phase with the run winding to provide starting torque for the motor. The RUN capacitor also provides โrunning torqueโ once the motor is up and running.
โSep-11-2019 06:48 AM
โSep-11-2019 05:18 AM
DFord wrote:
Just because the compressor is hot doesn't mean it's running. Can you hear it running? From what you've said, I don't think it's running.
The small tube coming out of it going to the condenser should be too hot to touch if it is running. If it isn't running, take a look at the capacitors. If the one in a metal can shows ANY sign of bulging, replace it. If there's one in a black plastic container, examine it for signs of damage - they can overheat very quickly and spew wax around before busting the plastic case open. If there's something that says "easy start" on it, it may have failed. The easy start and start capacitor get the compressor turning, the run capacitor keeps it running and reduces the amps drawn by the compressor.
โSep-11-2019 03:35 AM
DFord wrote:
Just because the compressor is hot doesn't mean it's running. Can you hear it running? From what you've said, I don't think it's running.
The small tube coming out of it going to the condenser should be too hot to touch if it is running. If it isn't running, take a look at the capacitors. If the one in a metal can shows ANY sign of bulging, replace it. If there's one in a black plastic container, examine it for signs of damage - they can overheat very quickly and spew wax around before busting the plastic case open. If there's something that says "easy start" on it, it may have failed. The easy start and start capacitor get the compressor turning, the run capacitor keeps it running and reduces the amps drawn by the compressor.
โSep-10-2019 08:04 PM
Ivylog wrote:
I would try replacing the run capacitor.
โSep-10-2019 07:53 PM
โSep-10-2019 03:41 PM
โSep-10-2019 03:01 PM
โSep-10-2019 12:54 PM
kmb1966 wrote:
About a 4 year old Dometic Penguin II. Fan comes on, I hear the compressor kick on, but air is warm. Removed the cover, and the compressor is too hot to touch, cold copper lines are not cold at all.