MJGenay wrote:
So I finished replacing the thermostat and I still have the same issue as before. Not much of an issue getting the pilot lit off but won’t make a larger flame than the pilot. Not cooling. I haven’t tried on AC yet this year. Any other ideas?
May-25-2023 01:46 PM
May-04-2023 10:17 AM
dougrainer wrote:
Your model refer has what is called a BYPASS LP TSTAT. That means when on LP, and you select your temp on the inside knob, the refer flame will go to "hi" when calling for cooling. When the temp is reached, the flame then goes to a smaller flame, but still blue. Since it works on 120(the mechanical point part of the tstat), the problem is a bad tstat on LP. Finding a 2400 tstat after 37 years will be difficult. I would do an extensive Google search for a Dometic RM 2400 tstat and see what comes up. A LONG shot would be to remove the tstat and attempt to clean it out. This would not affect the 120 side of the tstat. BUT!!!!!!!! If you decide to remove the tstat without having a replacement, be advised that the small capillary temp metal sensor tube that goes from the tstat to the inside metal evap fins may crack/break when attempting to remove to pull the tstat. After 37 years, that metal tube will be more brittle than new. IF that tube cracks/breaks, then the 120 side of the tstat will fail to function. Doug