ScottG wrote:
To the OP, as usual, a conversation regarding electrical questions has been taken down a long path with many detours and there are many wrong statements and frankly bizarre theory's bouncing around that's it's just not worth reading anymore.
Bottom line is just try it.
If it works, it works. if it doesn't, it doesn't (probably because of a GFCI).
As a career EE I can tell you there will be no harm either way.
โNov-14-2017 07:04 PM
โNov-14-2017 06:53 PM
โNov-14-2017 06:52 PM
โNov-14-2017 06:20 PM
โNov-14-2017 05:50 PM
DrewE wrote:
In theory, it can be done. If the 20A outlet (or the 30A one, for that matter) has a GFCI, it will trip due to the other neutral providing a second return path for the current...and rightly so.
In practice, I would strongly recommend against it. Particularly in some fault conditions, this can be a dangerous setup. If the neutral on the 30A circuit were to open and the two are on the same phase, you can have 50A flowing through the 20A circuit's neutral connection without a breaker tripping. That's a significant overload, enough to be reasonably worried about fire.
Putting the air conditioner on an isolated circuit that connects to the 20A outlet is a safer and IMHO better approach.
โNov-14-2017 05:39 PM
โNov-14-2017 04:27 PM
โNov-14-2017 03:49 PM
โNov-14-2017 03:14 PM
Bill.Satellite wrote:
The combiners do work but please understand that 50amp services provides you with 5 separate 50 amp legs or a total of 100 amps of service.