SHRED wrote:
Update:
Replaced brushes and springs.
Shined the rings.
That brought my stationary ohm reading into tolerance on the 9/10 pins at 25 ohms.
Problem is during spinning the ohms flucuate from 0.00 to OL at those same pins.
I think I have a short in the rotor.
โFeb-28-2021 08:33 AM
โFeb-23-2021 08:48 AM
โFeb-19-2021 12:16 PM
โFeb-19-2021 11:45 AM
โFeb-19-2021 07:17 AM
โFeb-18-2021 06:15 PM
โFeb-18-2021 01:22 PM
SHRED wrote:
Would a bad Automatic Transfer Switch cause the genset breaker to trip off?
โFeb-18-2021 01:05 PM
SHRED wrote:
Would a bad Automatic Transfer Switch cause the genset breaker to trip off?
โFeb-18-2021 01:03 PM
โFeb-18-2021 12:56 PM
SHRED wrote:I don't.time2roll wrote:
170v sounds like a regulator issue or an open neutral. Best to have a pro look at this issue.
I'm in Encinitas, CA (San Diego County).
Do you know of any good shops in my area?
โFeb-18-2021 10:41 AM
โFeb-18-2021 10:20 AM
KMLsquared wrote:
While I agree 170VAC is too high, I don't see why that would be tripping a over current device like a breaker. If all down stream loads are off and its tripping there must be a short between that generator breaker and the main breaker of the 120VAC distribution panel. Start tracing wires and opening junction boxes.
Odd the 170V as that is the peak voltage of 120VAC. Is your meter a good one or a cheap harbor freight one?