Skibane wrote:valhalla360 wrote:
With a large semi-permanent installation, you can move it further away and/or build a sound enclosure that negates the sound level.
The military just digs a pit, and drops the generator in it.
(Erecting a tarp over the pit is recommended in rainy weather...)
โNov-21-2021 10:40 PM
Gdetrailer wrote:valhalla360 wrote:Gdetrailer wrote:
In the OPs case..
2 RVs with 50A shore power = 24Kw
1 RV with 30A shore power 3.6Kw
Fair chance that the folks with 50A shore power will easily end up tripping the gen. Their rigs have a 50A breaker so they can draw 50A (6,000W) on each leg which means the generator breaker now becomes the limiting factor.
You are confusing the theoretical peak load with the realistic peak load. Most 50amp rigs never hit anywhere close to their theoretical peak.
30amp it happens but even there it's for a second or two then drops back to something closer to 10-15amps. As long as everyone's air/con compressor doesn't kick over at the exact same time, you can have a generator quite a bit lower.
Not "confusing" anything.
For all intents and purposes, the two RVs with "50A" shore connections are able to draw more power than the one that is 30A. The breakers on the gen now become the limiting factor.
A 6Kw gen can output a max of 25A at 240 or 2 120V at 25A each.
13.5K A/C when running will draw easily 13A (1560W)in the heat of the day not including startup surges. They will have a LRA current of 20A-29A (2400W-3480W)each. The LRA is why many folks struggle getting a 2Kw inverter gen to consistently start and run a A/C unit.
Typical 6Kw gens are combo 120V/240V, you can pull max of 25A at 240V or you have essentially two separate 120V only windings which provide 25A each.
if the 50A rigs were connected via a 50A-30A 120V adapter you have to stack two rigs on one 120V winding and one on the other 120V winding.
You could of course connect the 50A rigs to the 240V outlet but now you have two rigs stacked but yet the way 50A rigs are wired it will still have more loads on L1 than L2 and still have to share one leg heavily (generally the second A/C unit is put on the L2 circuit).
The result will still be someone losing out.
The fix is simple, either go much bigger than 6Kw or bring your own smaller gens. 9Kw-10Kw would be the min I would recommend, that gives you some hope that the two rigs stacked on the one leg will not easily trip the breaker on the gen.
Something else to consider when using 120/240 gens, uneven loading of the two 120V windings results in uneven and poor voltage regulation. The AVR samples from only ONE of the 120V windings resulting in rather poor voltage regulation if you stack the load unevenly (IE more load on the wrong winding).
โNov-21-2021 09:28 AM
valhalla360 wrote:
With a large semi-permanent installation, you can move it further away and/or build a sound enclosure that negates the sound level.
โNov-21-2021 09:25 AM
valhalla360 wrote:Gdetrailer wrote:
In the OPs case..
2 RVs with 50A shore power = 24Kw
1 RV with 30A shore power 3.6Kw
Fair chance that the folks with 50A shore power will easily end up tripping the gen. Their rigs have a 50A breaker so they can draw 50A (6,000W) on each leg which means the generator breaker now becomes the limiting factor.
You are confusing the theoretical peak load with the realistic peak load. Most 50amp rigs never hit anywhere close to their theoretical peak.
30amp it happens but even there it's for a second or two then drops back to something closer to 10-15amps. As long as everyone's air/con compressor doesn't kick over at the exact same time, you can have a generator quite a bit lower.
โNov-20-2021 11:11 PM
Gdetrailer wrote:
In the OPs case..
2 RVs with 50A shore power = 24Kw
1 RV with 30A shore power 3.6Kw
Fair chance that the folks with 50A shore power will easily end up tripping the gen. Their rigs have a 50A breaker so they can draw 50A (6,000W) on each leg which means the generator breaker now becomes the limiting factor.
โNov-20-2021 11:07 PM
Gdetrailer wrote:
Something else to consider, the bigger gen you go, the much louder it will be, somewhere I have a link to a video I took with a sound meter for my 8500W 13HP gen, very, very loud.. I use good quality hearing protection when I am near it when running.
โNov-20-2021 08:51 AM
pianotuna wrote:
I've never overloaded my yahama 3000sieb, except when deliberately trying to do so. To be fair, I do have a load support inverter/charger. The generator does have remote electric start and I use it sparingly.
I do use a watt meter--and on shore power I've never used more than 7200 watts peak load (how--I have 2 auxiliary shore power cords). Average load at -30 is about 4300 watts (per hour so 4.3 kwh). But we are talking summer time, and the living is easy.
My rv behaves as if it were on shore power full time.
I deliberately limit my 30 amp consumption to 23 amps, which is what the Yamaha outputs.
23 x 120 = 2760 watts peak load when boondocking.
โNov-20-2021 07:51 AM
Gdetrailer wrote:pianotuna wrote:13.5K AC 13A (1560W) run
Having done lots of power measurements during outages at my house, I found I could run all the important circuits from a 2800 watt kipor generator.
We tend to think of maximum loads--but really I could do fridge, freezer, furnace, most of the lights, router (for wobbly wide web) computers, laptop, garage door openner and block heater for the car. I used a manual transfer switch with six circuits. the Kipor did not overload even once.
RV fridge heater approx 300W
electric heating element in water heater 1200W
converter charging batteries up to 1200W at full load (supporting battery charging duties plus 12V appliances and lighting)
Entertainment, 200W for average LED backlit TV of 32"+ size
A potential of 4150W
โNov-20-2021 06:30 AM
pianotuna wrote:
Having done lots of power measurements during outages at my house, I found I could run all the important circuits from a 2800 watt kipor generator.
We tend to think of maximum loads--but really I could do fridge, freezer, furnace, most of the lights, router (for wobbly wide web) computers, laptop, garage door openner and block heater for the car. I used a manual transfer switch with six circuits. the Kipor did not overload even once.
โNov-20-2021 03:55 AM
โNov-20-2021 01:14 AM
LouLawrence wrote:
50 amp service equals 12,000 watts (2 legs of 50 amp = 100 amps @ 120V) x 2 vehicles equals 24,000 watts. Add in the 30 amp coach at 3600 watts and you need 27,600 watts to properly service all 3 RV's. You would need a substantial generator to supply the power to all 3 and that would be done by feeding the service from this 30,000+ watt generator to a sub-panel from which you could run 3 proper circuits to 3 independent plugs that the RV's could plug into.
โNov-19-2021 08:51 PM
Michelle.S wrote:
If the area is at all remote, I doubt the Generator would be there long before it developed legs and wandered off the property.
โNov-19-2021 07:40 PM
โNov-19-2021 06:05 PM
โNov-19-2021 05:25 PM