BFL13 wrote:
What is the actual set-up, to clarify the situation?
โApr-16-2018 04:45 PM
โApr-16-2018 04:36 PM
time2roll wrote:
These GFCI generally trip in excess of 5 mA differential. Could be you each are leaking 2 mA.
I would first try turning off all breakers in the RV except the main and the charging system. See if that eliminates something.
Second I would try using a Battery Minder or Battery Tender brand maintenance charger direct from the outlet to the battery and see if that resolves the issue. The idea is to remove all the RV circuitry from the load circuit.
Otherwise could prove difficult unless you have the keys to all three RVs.
100+ watts solar and a controller could also eliminate the need to plug in.
โApr-16-2018 04:25 PM
SoundGuy wrote:mikestock wrote:
I still think something is going wrong with the GFIC breaker but I'm no expert. May go buy one myself and changing it out.
If you do you'll have more luck if you buy a GFCI. ๐
โApr-16-2018 04:21 PM
โApr-16-2018 04:19 PM
โApr-16-2018 04:08 PM
โApr-16-2018 04:04 PM
mikestock wrote:
I still think something is going wrong with the GFIC breaker but I'm no expert. May go buy one myself and changing it out.