Hydro Flame 8500-11 Furance problem

arkansasrunner
Explorer
Explorer
Just had to shut the furnace down. It is blowing real hot. The air is so hot that it melted my register vents. & is so hot, you can not keep your hand on them. I read that it is supposed to shut down at 180 degrees, but I don't think it is. Could this be a bad Limit Switch ? Or something else ? Thanks
1994 Ford F250 4 Wheel Drive Deisel
1991 NewMar Kountry Star 30'
4 REPLIES 4

arkansasrunner
Explorer
Explorer
I don't think that it has been bypassed. I have had this 5th for 6 years & the furance has always worked fine.Think I better call in a tech to see what the problem is.
1994 Ford F250 4 Wheel Drive Deisel
1991 NewMar Kountry Star 30'

Old-Biscuit
Explorer III
Explorer III
YES the 'high limit' switch should kill all power to furnace should temps go over 190*F

Part # 37022
Limit Switch L190ยฐ
Is it time for your medication or mine?


2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
US NAVY------USS Decatur DDG31

hypoxia
Explorer
Explorer
Hydroflame manual
Hydroflame manual #2
Jim

2007 Monaco Signature Noble III ISX 600HP

dougrainer
Nomad
Nomad
Yes, the Hi limit switch is stuck CLOSED and is not letting the furnace burner do its normal cycle on and off. Replace the Limit. BTW, I have never seen a furnace limit stick ON in 35 years of repairing RV's. Is it possible someone has bypassed the hi limit and that is why it stays on? Doug