inverter power cables cca or ofc

Bigfoot2005
Explorer
Explorer
What type of power cables can be used for battery connections to 1500 watt inverter?

CCA or OFC
31 REPLIES 31

time2roll
Nomad
Nomad
Now look at the graph at the 200% level. Close to a minute to open. That is 400 amps close to a minute before that 200 amp class T opens. Your call.

Search for ANL and you will see much faster open at 200%.

Bigfoot2005
Explorer
Explorer
time2roll wrote:
200 class T is fine. I would use 150 amp. That is all I am saying.

GP also say #2 wire and 2/0 is getting installed.



https://www.bluesea.com/products/5112/Fuse_A3T___Class_T_110_Amp

Ampacity of #2 with 105C insulation is 210 amps
Ampacity of 2/0 with 105C is 330 amps

http://www.genuinedealz.com/voltage-drop-calculator


They suggested 2/0 wire to me if I am going to do a longer run of wire as I might have too to avoid a voltage drop

time2roll
Nomad
Nomad
200 class T is fine. I would use 150 amp. That is all I am saying.

GP also say #2 wire and 2/0 is getting installed.



https://www.bluesea.com/products/5112/Fuse_A3T___Class_T_110_Amp

Ampacity of #2 with 105C insulation is 210 amps
Ampacity of 2/0 with 105C is 330 amps

http://www.genuinedealz.com/voltage-drop-calculator

Bigfoot2005
Explorer
Explorer
time2roll wrote:
Class-T will pass 2x rating for 60 seconds. That 1500 would have to draw 300 amps for a full minute to open. Not going to happen during normal operation. Check Blue-Sea graph.


Not sure what you are saying. The manufacturer recommends the Class T fuse rating of 200 amps for their 1500 watt inverter.

1100 โ€“ 1800W inverters 200 amp #2 AWG

time2roll
Nomad
Nomad
Class-T will pass 2x rating for 60 seconds. That 1500 would have to draw 300 amps for a full minute to open. Not going to happen during normal operation. Check Blue-Sea graph.

MEXICOWANDERER
Explorer
Explorer
Then so be it. They are the Supreme Court. Cheap inverters have little or no reserve punch and the manufacturer knows their product. ๐Ÿ™‚

Bigfoot2005
Explorer
Explorer
MEXICOWANDERER wrote:
Too tight of protection may blow a fuse. How? Inverters are rated for overcurrent to start a load that draws a lot more than nameplate design. My recommendation if to check with the manufacturer or vendor.

My Trace is rated to start stuff to nameplate rating times eight.


Manufacturer recommends 200 amp T fuse for the 1500 watt inverter

MEXICOWANDERER
Explorer
Explorer
Too tight of protection may blow a fuse. How? Inverters are rated for overcurrent to start a load that draws a lot more than nameplate design. My recommendation if to check with the manufacturer or vendor.

My Trace is rated to start stuff to nameplate rating times eight.

time2roll
Nomad
Nomad
200 amp ANL is fine. I would go a little tighter with Class-T with 150 amps.

ktmrfs
Explorer II
Explorer II
GordonThree wrote:
Spend a bit more and get a class T fuse and holder. Look at the short circuit current of your battery bank and the interrupt capability of the fuse.


x2. and mount it as close to the battery as possible.
2011 Keystone Outback 295RE
2004 14' bikehauler with full living quarters
2015.5 Denali 4x4 CC/SB Duramax/Allison
2004.5 Silverado 4x4 CC/SB Duramax/Allison passed on to our Son!

GordonThree
Explorer
Explorer
Spend a bit more and get a class T fuse and holder. Look at the short circuit current of your battery bank and the interrupt capability of the fuse.
2013 KZ Sportsmen Classic 200, 20 ft TT
2020 RAM 1500, 5.7 4x4, 8 speed

Bigfoot2005
Explorer
Explorer
Thanks to everyone for your help and input.

I am also wondering what sort of fuse do you guys use? I am use to installing car stereos and using ANL inline fuse. Will these also work with for inverter protection? Looking at a 200 amp inline fuse with 2/0 welding cable.

time2roll
Nomad
Nomad
See manual p23
(note copper wire only)


The distance between the battery bank and the GP-ISW should be as short as possible to achieve maximum efficiency and to reduce fire hazards. The size of the cable should be thick enough to limit the voltage drop to less than 2% when carrying the maximum input current to prevent frequent low-input voltage warnings and shutdown. Only use high quality copper wire.
For greater efficiency, the cables should be as short as possible. The combined cable length should be no more than 10ft (3m). Keeping your wire runs as short as possible helps to prevent: low voltage shutdowns and nuisance tripping of the DC breaker because of increased current
draw. The table below shows the recommended DC cable size, fuses/circuit breakers and DC grounding cable sizes for the GP-ISW (Note: these values are correct for cables in free air, not conduit)
Model Wire AWG Inline Fuse / Circuit Breaker

GP-ISW1500-12 #2 F-200A

pianotuna
Nomad III
Nomad III
No aluminum wire. 15 feet may need 1/0 wire.

Move the inverter closer.
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.