bucky wrote:
If going thru all that why not put in 20/30/50? Who knows what the future brings.
โAug-14-2018 04:30 AM
โAug-14-2018 03:50 AM
โAug-13-2018 07:06 PM
Boomerweps wrote:
I'm looking at Direct Burial wire or interior grade that would be routed through sealed plastic pipe. I've only checked Home Depot pricing so far and not the local electrical supply house.
Garage has 12awg run to it and is a good 110-120 feet run through the house and ground from the CB box.
โAug-13-2018 06:38 PM
โAug-13-2018 06:20 PM
โAug-13-2018 05:51 PM
enblethen wrote:
I would suggest replacing the feed to the garage and then installing the RV receptacle off that.
You could use RHH/RHW/USE wire which is rated for direct burial. I would use #6. Yes, slightly overkill(50 amp). yes, #8 would work(40 amp).
The ground wire can be smaller. It would be calculated on the amperage of the circuit breaker in the source panel. A #10 ground wire would be sufficient for up to 60 amp circuit breaker.
I would install and additional ground rod at the detached garage for a little extra protection.