Onan generator shorted (110 side)

vacuumbed
Explorer
Explorer
Hello everyone.

My 1978 Pace Arrow developed an issue. When the shore cord is pugged in to power it will trip the residential house breaker immediately.

I traced it to the generator, which is an Onan 6.5 gas unit. The Hot and the Ground has full continuity! This can't be right. Has anyone heard of this issue?

I'm thinking the voltage regulator is blown or there is a problem in the generator itself.
36 REPLIES 36

vacuumbed
Explorer
Explorer
It's 30 amp service.

I can put it back the way it was, but my concern is that something is damaged in the generator.

wolfe10
Explorer
Explorer
On that age coach, I am ASSUMING that it is 30 amp, not 50.

Wiring to the ATS is very simple:

Three wires in from shore power: hot, neutral and ground.

Three wires in from generator: hot, neutral and ground.

Three wire out to coach 120 VAC breaker box: hot, neutral and ground.

How did you wire it?

BTW, if 50 amp, add another hot to each (shore, generator and out to breaker box).
Brett Wolfe
Ex: 2003 Alpine 38'FDDS
Ex: 1997 Safari 35'
Ex: 1993 Foretravel U240

Diesel RV Club:http://www.dieselrvclub.org/

copeland343
Explorer
Explorer
Put the wiring back the way it was and then try it. Also on some RVs the generator does not power up everything to much load.

vacuumbed
Explorer
Explorer
Anyone?

vacuumbed
Explorer
Explorer
It has an ATS. I rewired it because only half of the breakers were hot when plugged in to shore power. Did I damage my generator?

ScottnSherrie
Explorer
Explorer
My rig is an 88 and there is no switch for connecting to the genset. There is an outlet in the power compartment that is wired to the genset. How do you connect genset power to your rig?
88 Gulf Stream 34' Sun Vista, Ford 460, Edelbrock Perfomer carb, Thorley headers
Ford F-250 crew cab 4X4, 6.0 turbo diesel
complete roof rebuild
daughter 19, son 16
US Army Desert Storm vets (both of us)
left: The Ol' Gal right: DW with White Lightnin'

wolfe10
Explorer
Explorer
Do you have an ATS (Automatic Transfer Switch) or do you have to manually change from shore power to generator power?

Both sources should NEVER be used at the same time. So, even if the generator is shorted, shore power should never reach it.
Brett Wolfe
Ex: 2003 Alpine 38'FDDS
Ex: 1997 Safari 35'
Ex: 1993 Foretravel U240