CA Traveler wrote:BFL13 wrote:
No, this is with the battery bank as 12v. The 55 and the 75 run perfectly from the Honda 3000 individually, but add one to the other and it pops the Honda's overload, but the engine keeps running. Then you have to shut down the generator's engine and start over as how to reset it.
Something is not right. Those two chargers by themselves are no where near the gen capability.
So bad gen, connection problem, bad charger, other loads, cockpit problem or something else???
โJan-01-2017 08:02 PM
โJan-01-2017 07:52 PM
BFL13 wrote:Something is not right. Those two chargers by themselves are no where near the gen capability.
No, this is with the battery bank as 12v. The 55 and the 75 run perfectly from the Honda 3000 individually, but add one to the other and it pops the Honda's overload, but the engine keeps running. Then you have to shut down the generator's engine and start over as how to reset it.
โJan-01-2017 06:25 PM
โJan-01-2017 03:52 PM
time2roll wrote:BFL13 wrote:is it a load issue or a GFCI issue?
The no go with 55 and 75 is a puzzle. It pops the breaker(s) immediately.
Set the voltage same as the battery (26v?) and try again.
โJan-01-2017 03:28 PM
BFL13 wrote:is it a load issue or a GFCI issue?
The no go with 55 and 75 is a puzzle. It pops the breaker(s) immediately.
โJan-01-2017 02:25 PM
pianotuna wrote:
Hi BFL13,
The Honda can only do that "over" wattage for 30 minutes--then it may shut down to protect itself. It can do that because the no load output is 127 volts.
It won't do the 75 and 55 because neither is power factor corrected?
โJan-01-2017 12:11 PM
โJan-01-2017 09:45 AM
time2roll wrote:
Yes put the 75 and 55 in parallel and that group in series with the 100 amp.
This will get you 100 amps at 24 volts.
I can't wait for the testing ๐
I still recommend matching the chargers or even better just get a 24 volt converter.
โJan-01-2017 09:32 AM
โJan-01-2017 09:20 AM
โJan-01-2017 09:03 AM
โJan-01-2017 09:00 AM
โJan-01-2017 08:59 AM
2oldman wrote:BFL13 wrote:I'd have to say (55 x 12) watts.
If in fact the 100 is adding its voltage, but no amps, what would its draw on the generator be?