Hi all.
I am in proses of installing solar on my FW I planed on installing 2
/150W panels but made mistake when ordering and ordered 2 lots of 2 so have got 4/150W panels, also got 30' of 8AVG cable to split to my trimetric sc 2030 controller and 2030 monitor. cable is rated for 600v so is this a little to small or will it be ok. Al panels max 36A at 16' to controller .7219v drop or 4.0108% drop.2 260A 6V Crown Batteries what are your thoughts.
Frank.
Frank
2012 F250 XLT
4x4 Super Cab
8' Tray 6.2lt, 3.7 Diff.
36 REPLIES 36

Almot
Explorer III
Explorer III
Slownsy wrote:
It seams ther is as manny different opinions as peaple out there.

"Options", not "opinions" :). There are different ways to use what you have. And different scenarios of use.

Normally, people with this type of controller are trying to keep a safety margin, so that panels won't generate more current than controller could handle. It can get too hot, and controller will fail under 30A load. "Probably" with 3 panels you won't exceed the 30A limit, with dust on panels and losses in wires. Or it can get too cold and/or you camp at high altitudes and panel current will spike. Too many "ifs" to my taste. The manual does say "May be safely used with panels up to 60A, however charging current will be reduced to protect charger". A 30 PWM controller with built-in 100% safety margin? Not 20%? Maybe. Can't say. You are one of very few people that bought this controller.

You can't have 4 panels without getting a bigger controller. Again, "normally", people are trying to get a margin here as well, installing a bigger controller and beefier cables than their array requires, with possible extra panels in mind. Adding a 2nd controller and separate parallel set of wires will be a royal pain in the ars.

Slownsy
Explorer
Explorer
Hi all thanks for the input, special thanks to grizzzman, I have read what the instructions mention and was planing to contact Bogart but you saved me the trouble, will go ahead with the 3 panels for now and se what controler tels me with only the 3 my cable run to my breaker only about 10' and will use 6AVG from ther and to controler and 2 AVG to batteries,and maybe instal last panel with sepret controler later.
It seams ther is as manny different opinions as peaple out there.
Frank.
Frank
2012 F250 XLT
4x4 Super Cab
8' Tray 6.2lt, 3.7 Diff.

Almot
Explorer III
Explorer III
jrnymn7 wrote:
I wouldn't go with 24v panels at anything less than 460w, flat mounted, myself. Which is probably pretty close to what a 12v 300w pointed array would do.

Yes and no. In mid-summer the difference in harvest between flat and tilted is ~30% or less, so 300W tilted will harvest less than 460W flat. Besides, tilt is usually to one side only, and you don't always park with that side to the South. In Southern states I would say 300W tilt-able will collect less than 460W flat. In winter titled 300 could beat 460 flat, especially up North.

24V panels start at ~180W, so a pair of them would be pretty much +400W. With size (and often price too) of 200W panel being the same as 250W, and MPPT controllers being tolerable to current over its rated limit, it indeed makes makes sense to max it up to 480-500W.

Roof-mounted tilt-able and point-able arrays have fallen out of favor lately, with panel prices low. Especially point-able, i.e. with adjustable azimuth - too complicated, and a pain climbing up and down.

jrnymn7
Explorer
Explorer
I wouldn't go with 24v panels at anything less than 460w, flat mounted, myself. Which is probably pretty close to what a 12v 300w pointed array would do.

jrnymn7
Explorer
Explorer
My only concern about exceeding any controller's current rating, would be the heat being generated by doing it. Additional ventilation would now be required; perhaps even more-so with the larger units available, like say 45 amps and up.

Almot
Explorer III
Explorer III
jrnymn7 wrote:

At a 30 degree angle of incidence, the 4 panels can still put out about 90% of their Isc. At 45 degrees, about 80%. That's over 32a, and about 29a, respectively. So using all 4 panels is too much.

That's why for +300W I prefer 24V panels and MPPT controller. Most users do, I think. No worries about exceeding the controller current rating, and parallel wiring becomes optional.

jrnymn7
Explorer
Explorer
BFL said,

"A panel will do its Isc (ignore the lower amp Imp for MPPT) at STC when the panel is aimed at the sun. So how much less you get when the panel is flat depends on how high the sun gets where you are at what time of year.

You can be far enough South in the summer that your flat panel will hit its full Isc rating."

At a 30 degree angle of incidence, the 4 panels can still put out about 90% of their Isc. At 45 degrees, about 80%. That's over 32a, and about 29a, respectively. So using all 4 panels is too much.

Almot
Explorer III
Explorer III
jrnymn7 wrote:
OP, if you're set on using the 30a trimetric controller, then install 3 panels flat, run that 8ga on both sides of the controller, for some intentionally engineered efficiency loss / voltage drop,

Yep. 3 is less than 4, but since he insists on having less power...
Before controller, in this case, I would run MC4 AWG 8. With MC4 Y-splitters. No messy rooftop junction boxes.

Almot
Explorer III
Explorer III
smkettner wrote:
The monitor will tell the controller when the battery is full. This allows for automatic extended absorption time during heavy use and very short absorption when in storage or light use. No sense in having the battery at 14.8 volts three hours every day when in storage. Like wise some controllers drop to float as soon as they hit the voltage set point and will be a bit weak while in use.

Crutches. Using another device to help this one to work properly.

I have a current-based end of absorption on my controller. Heavy use - high current - absorption extends until heavy use is over. Light use - low current - absorption ends sooner. And simultaneously there is a timer-based absorption end, to end the struggle if it drags too long. Timer overrides the current-based end, i.e. when timer expires, absorption ends no matter what. Timer is adjustable too, of course. Very flexible firmware.

grizzzman
Explorer
Explorer
Slownsy wrote:
Ok tanks all yes I ment 4/150Watt panels, only planed on getting 2 but as I now have the 4 and the room for them, someone mentinned that the trimatik wood handle the extre load ok as they will be mounted flat and properly newer reach ther full potential, they are Renogy 150 W mono crystalline.
I can go to larger wier and stay with 3 panels if this what most recommend and try to sell last panel.
Frank.


Hi Frank
It is good to get advice on what to do but remember no one here has said "I have one and this is what it will do". Look at your manuel, it states that it will handle 4 135 watt panels. Thats 540 watts. In the specs page it states " Solar-panel peak current max 31 amps for peak efficiency. May be safely used with panels up to 60 amps, however charging current will be reduced to protect the charger".

With that being said here is an E-Mail reply from Ralph Hiesey the founder and owner of Bogart Engineering earlier this month that i feel applies.

Hello again, Miles
We intend to get a graph of the temp comp on the website soon. I have included an attatchment of this in the e-mail. I agree we need to make this easily accessible.

Even at 30 amps the heat sink should be ok up to 130F or so (ambient environment). Keeping it cooler would be better for longest life, however.(the temperature of the regulating transistors on the heat sink is of no concern-but the electrolytic capacitors on the pc board at high temperature could suffer in the long term) But if you are running 20 amps or less of panels it would be difficult to ever get it too hot. If at or over the 30 amps maximum try to insure the ambient temp is less then 120F. (Of course if over 31 amps the charger will reduce its output to protect itself-but will get hot)

Yours truly
Ralph H.

As you can see you could "overpanel" but you would have to be "VERY" careful with thermo management or you will shorten the life or kill the controller.
I personaly would not have a problem with running 3 panels on this controller.
Your 8AWG wire is just plain to small. Again look at the manuel i have already given my wiring recomendation in a previous post. Use the 8AWG wire on the single panel and pick up a cheap controller, problem solved ๐Ÿ™‚
2019 Ford F150 EcoBoost SuperCrew
2016 Rockwood Mini Lite 2504S. TM2030 SC2030
640 Watts Solar. Costco CG2 208 AH and Lifepo4 3P4S 150 AH Hybrid. ElectroDacus. Renolagy DC to DC charger. 2000 Watt Inverter.
Boondocking is my Deal

jrnymn7
Explorer
Explorer
OP, if you're set on using the 30a trimetric controller, then install 3 panels flat, run that 8ga on both sides of the controller, for some intentionally engineered efficiency loss / voltage drop, and call it a day. (Or just install 2 panels for about the same results at the batteries).

time2roll
Nomad
Nomad
Almot wrote:
smkettner wrote:
The beauty of the Trimetric 2030 is that it ties into the battery monitor to better control the charge rate.

I don't understand about this being tied into monitor for better control.
The monitor will tell the controller when the battery is full. This allows for automatic extended absorption time during heavy use and very short absorption when in storage or light use. No sense in having the battery at 14.8 volts three hours every day when in storage. Like wise some controllers drop to float as soon as they hit the voltage set point and will be a bit weak while in use.

Excellent system IMO. Morningstar adjusts absorption based on the start voltage of the day but this Trimetric sounds even better.

Almot
Explorer III
Explorer III
Slownsy wrote:
I have got what I have which is a great controler and monitor with temp censer, I do not intend to change controler,

You also have got 4 panels, so why not using them. Even if this will lead to changing the controller or adding another one. I would rather got a bigger controller than add another one in parallel. Routing cables is a pain, inside RV space is limited, and a second controller won't make it easier.

Higher capacity controllers that were mentioned here, have a temp sensor too. With your planned trips from Florida to Alaska temp sensor is important.

Flat panel in winter, even in AZ, will collect 1.5-1.7 times less energy than a tilted one.

One thing you didn't mention is WHAT you need your solar for. Occasional charging when opportunity presents itself, without relying on it - like BFL does - is one thing. Charging mostly off solar is another. To figure out whether you need 2 or 4 panels (leaving aside the controller issue), you need to answer this, and also to estimate your daily amp-hour use as others here noted. Since you have a battery monitor, this shouldn't be a problem.

Westend wrote:
For the controller to batteries, I'd use the same AWG 4, depending on the length of run to the batteries.

Or AWG 6. Depends on the length of run. If he decides on mere 2 panels, there is a good chance that AWG 6 will do.

EsoxLucius
Explorer
Explorer
westend wrote:
OP states he has two 6V Crown batteries @260 AH. The length of the run from modules to controller is 16'. He does not say what length of run is from the controller to batteries.
If it was me, I'd use #10 MCA cable from the modules to a combiner box on the roof and then run AWG 4 from the box to the controller (interrupting it with a circuit breaker mounted close to the controller). For the controller to batteries, I'd use the same AWG 4, depending on the length of run to the batteries. I tend to use larger wire than most but I reasoning is that I'd rather pay a few dollars more for wire, initially, than give up solar harvest eternally.
I like this response but am even more anamoured with thicker wire between the controller and the batteries.
2013 LTV Unity MB Theater Seats
635 watts solar panels, 440 AH batteries, BlueSky Solar Boost 3024iL & IPN-Pro Remote, Magnum MS2000 & ME-RC50 remote
Koni Shocks F & R, Hellwig 7254, SumoSprings F & R
2012 Hyundai Accent SE, Blue Ox Aladdin/Patriot