clotus wrote:BFL13 wrote:
The neg wire output from the solar controller has to go to the Trimetric shunt same as all the other negatives, for the Tri to "read" that. It sounds like you have that wire going to the neg battery post and not via the shunt.
I think you are absolutely right!!! Why didn't I think of that. I will re-wire it tomorrow and see if that fixed it.
My last install used the trimetic meter along with their solar charger (SC-2030) and I had the cables directly on the batter, but because they communicated it probably worked properly despite not being wiring properly.
โMar-21-2018 01:34 PM
BFL13 wrote:
The neg wire output from the solar controller has to go to the Trimetric shunt same as all the other negatives, for the Tri to "read" that. It sounds like you have that wire going to the neg battery post and not via the shunt.