Old-Biscuit wrote:Ottawa Campers wrote:
Hi all. I am looking for some help diagnosing a problem with my suburban SW6DE water heater. It has worked fine for 12 years but now it won’t run on gas.
When I turn the switch to start the propane burner nothing happens - no light on the reset button, no ticking of the igniter, nothing. I have 12 volts at the switch, the thermostat hi limit switch is fine, and I even get 12 volts at the red wire going into the module board with the propane switch in the on position.
I don’t really know what to do from here, so any advice would be appreciated.
Darryl
12V DC on RED wire AT the circuit board means DC circuit is good thru on/off switch, thru set of t-stats BUT nothing from circuit board
With DC on RED wire at circuit bd then should be DC on BROWN Wire to Gas Valve Solenoids and energizing the spark electrode with high voltage.
Check the YELLOW Wire coming out of circuit bd..GROUND and needs to be connected for circuit bd to function
Good ground.then circuit bd is Bad
Jul-30-2018 08:13 PM
Ottawa Campers wrote:
Hi all. I am looking for some help diagnosing a problem with my suburban SW6DE water heater. It has worked fine for 12 years but now it won’t run on gas.
When I turn the switch to start the propane burner nothing happens - no light on the reset button, no ticking of the igniter, nothing. I have 12 volts at the switch, the thermostat hi limit switch is fine, and I even get 12 volts at the red wire going into the module board with the propane switch in the on position.
I don’t really know what to do from here, so any advice would be appreciated.
Darryl
Jul-30-2018 06:32 PM
Jul-30-2018 06:25 PM
Jul-30-2018 05:50 PM
Jul-30-2018 05:13 PM
Jul-30-2018 05:08 PM